Hi I am recently qualified and still have a lot of learning/reading to do but Blue plastic waterpipe incoming, seems to always be a grey area with electricians I work with, me personally wouldn’t bond it..... Although we have to prove that in the plumbers install their is no copper going to earth?? Can someone enlighten me on this please

Many thanks..... and go easy on me lol
 
basically, you need to determine if any metal water pipes are extraneous. i.e. are they connected physically to the mass of earth. to do this, you set your MFT to IR test. test between the suspect pipe and your MET. if the reading is > 22k Ohms, then it does not require bonding.
 
basically, you need to determine if any metal water pipes are extraneous. i.e. are they connected physically to the mass of earth. to do this, you set your MFT to IR test. test between the suspect pipe and your MET. if the reading is > 22k Ohms, then it does not require bonding.

So does that mean only if they are accessible? And what if the blue plastic goes straight to white plastic? Would we have to take the bond over to the copper?
 
It’s highly unlikely that a mains water pipe entering a property in blue plastic then to copper will introduce an earth potential to the property unless said copper pipework is perhaps buried at some point in the ground.
Also when I ever see plastic incomers joining to copper say in commercial buildings and flats,the copper eventually joins to plastic again so it’s never necessary to provide protective bonding.
 
Of course there is the other viewpoint. In some point in the future that pipework after the plastic might be come ''extraneous' through refurbishments etc, so if you don't bond it from new (and it might get 'earthed' from parallel paths), and 10 years down the line it does become extraneous and requires bonding, how do you get a cable from the front to the back of the property. Just bond, and forget.
 
Of course there is the other viewpoint. In some point in the future that pipework after the plastic might be come ''extraneous' through refurbishments etc, so if you don't bond it from new (and it might get 'earthed' from parallel paths), and 10 years down the line it does become extraneous and requires bonding, how do you get a cable from the front to the back of the property. Just bond, and forget.
interesting viewpoint but you cant bond to start with if its plastic and you cant really forecast what might happen in future
 
Of course there is the other viewpoint. In some point in the future that pipework after the plastic might be come ''extraneous' through refurbishments etc, so if you don't bond it from new (and it might get 'earthed' from parallel paths), and 10 years down the line it does become extraneous and requires bonding, how do you get a cable from the front to the back of the property. Just bond, and forget.
When the 18th is published it looks like they have put it in black and white that if the incomer is plastic then doesn't need bonding.
 
It’s strange that every new build I see has now ditched the bonding to the water pipe as it’s plastic everywhere anyway but the gas still connects to the wall mounted meter outside in yellow plastic pipe.
Enters the property in copper but can’t see how it’s extraneous in that way?
Perhaps when the 18th is published they might not provide bonding to the gas anymore?
 
Hi I am recently qualified and still have a lot of learning/reading to do but Blue plastic waterpipe incoming, seems to always be a grey area with electricians I work with, me personally wouldn’t bond it..... Although we have to prove that in the plumbers install their is no copper going to earth?? Can someone enlighten me on this please

Many thanks..... and go easy on me lol
 
Thought that might generate some replies, by the way I wasn't suggesting bonding a plastic pipe.

All most every domestic dwelling I work in with a plastic water service and copper internals, has the copper bonded. This isn't new builds. Now that may be 'cos we've always done it that way, or ignorance, or because it was tested and found not to be extraneous.

So not bonding the metal element of a water service is correct, if when tested, is found not to be extraneous. What then if additional appliances (requiring cpc) are connected, which could change the results of that test, or the pipework is altered with the same result.

How do you now get a suitable cable to that point to bond it. How many of you test an existing install, to see if the existing pipework is extraneous, removing the water bond if necessary?

Not saying I'm right, just interested in the views of my more learned colleagues.
 
I think you will find that it says "if the water / gas pipe enters the house is of plastic construction, and the rest of the pipework is copper, then this copper must be bonded, are we not getting our wires crossed with the > than 22Kohms refers to supplementary bonding, not main bonding, open for discussion?
 
If you cannot prove it isn’t then yes.

Turn it on it’s head, would it be correct not to?

Ah but you originally (#17) said it's sometimes easier to bond it than to prove it, implying that you wouldn't bother testing.
 
I think you will find that it says "if the water / gas pipe enters the house is of plastic construction, and the rest of the pipework is copper, then this copper must be bonded, are we not getting our wires crossed with the > than 22Kohms refers to supplementary bonding, not main bonding, open for discussion?
no.the 22k ohms is to prove whether or not a piece of copper /metal pipe is extraneous or not.
 
no.the 22k ohms is to prove whether or not a piece of copper /metal pipe is extraneous or not.
Agree but is also used to prove that something is "extraneous" the pipework should be main bonded, but not bonded because it may be or maybe not classed as extraneous.
 

Attachments

Last edited:
I do find reg. 544.1.2 a bit confusing therefore, i.e. if the service is plastic the continuing internal metal does not need bonding argument? Or is the reg poorly worded and not drawing reference to extraneous or not.
 
On the other thread
Equipotential Bonding Explanation - https://www.electriciansforums.co.uk/threads/equipotential-bonding-explanation.136192/
if the metal pipework is not bonded, because the incoming service is plastic, when the kettle casing becomes live, the pipework may be not at the same PD, but could be earthed via parallel paths, so at the moment of the fault 'the touch voltage that may be experienced during a fault, i.e. for the 0.4s before the automatic disconnection occurs' (mentioned by RB) may be increased?
 
So is this topic a grey area in general lol I can never find or hear a straight answer for it as I have also heard that bonding something that doesn’t need a bond will possibly start a not needed potential??
 
It's not a grey area. If it's an extraneous conductive part it needs bonding. If it's not an extraneous conductive part it doesn't need bonding. I always run a green and yellow in for gas and water on a new builds as I've had muppet meter fitters refusing to connect as no bonding, even though it didn't require bonding. If they moan I connect it then chop it off when the muppet has finished.
 
Must admit, I'm still confusing myself over this. I understand the testing to conclude if a metal pipework after a plastic service is extraneous or not.

I take spinlondons point that bonding the above, under fault conditions may momentarily 'increase the number of conductive parts that will become live', but wouldn't these be earthed anyway by a circuit cpc?

The OSG recommends bonding of above, unless its been confirmed said pipework is not introducing Earth potential. It mentions pipework 'liable to introduce earth potential'. It doesn't mention testing to prove whether such pipes are extraneous, only gives examples, as in reg 411.3.1.2. Indeed the formulae for when doubt exists over effectiveness of extraneous or not, reg 415.2.2 is for supplementary bonding, something completely different. Reg 544.1.2 states where the consumers hard metal pipework should be bonded after insulating section or insert.

So I'm suggesting BS7671 recommends that unless you can physically confirm all such pipework is not liable to or not able to, then it should be bonded?
 
I don’t bother with the OSGs, as they contain so many errors.

Are you stating that the OSGs recommend bonding non-extraneous conductive-parts?
 
But it does contain some pretty pictures for us plebs. :)

Have a shufty yourself, it talks about it on pages 44 & 46 in the yellow version.
Unfortunately, that is not possible.
I only have a brown 16th and a red 17th someone gave me.
My point is however, BS7671 requires protective bonding for extraneous conductive-parts, not for non-extraneous conductive-parts.
 
Yellow OSG Sec 4.5 'Main protective bonding of plastic services'. There's no shock here (excuse the pun), it says there's no requirement to bond plastic services.

Continuing on page 46; 'Where there is a plastic service and a metal installation within the premises, main bonding is recommended unless it has been confirmed that any metallic pipework within the building is not introducing Earth potential (see 4.3, (referencing to reg 411.3.1.2).

I have had a quick shufty through GN8, and can't seem to find specific mention of the above scenario.

What do you make of the definition of extraneous-conductive-part in BS7671?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Hampshire

Thread Information

Title
Bonding gas/water yellow and blue
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
128
Unsolved
--

Advert

Thread statistics

Created
Houndogg10,
Last reply from
Deleted member 26818,
Replies
128
Views
19,669

Advert

Back
Top