atkins_1

Can someone answer this for me plz.
Do I need to bond to the gas metre where the pipe is completely on the outside of the house except where it enter through the brick work into the boiler?
Someone said no because its doesn't count as an extraneous conductive part.

Also the same house has a plastic incoming supply to water, brass stop cock then plastic pipe up to the boiler where it meets the water pipes for the whole house which are copper throughout.

For both gas and water I was told to disconnect any parallel earth paths and take a reading between the met and the gas pipe as it enters the house at the boiler. Same test between the met and the t'd off water pipes.

Something about gutting over 22k ohms and its okay to not bond? I was told an r2 for both the above. Got open circuit all round which I expected can Someone clear this up please.

Seems to be a grey area as I have asked around already.

Cheers
 
Do I need to bond to the gas metre where the pipe is completely on the outside of the house except where it enter through the brick work into the boiler?
The pipe must be bonded where it enters the premises.
Because it is connected to the boiler it will be earthed but should be main bonded to the MET.

Someone said no because its doesn't count as an extraneous conductive part.
Well, it is.

Also the same house has a plastic incoming supply to water, brass stop cock then plastic pipe up to the boiler where it meets the water pipes for the whole house which are copper throughout.
Not extraneous then.

For both gas and water I was told to disconnect any parallel earth paths and take a reading between the met and the gas pipe as it enters the house at the boiler. Same test between the met and the t'd off water pipes.
You could do that to be certain but no one is going to go to the bother.
So, normally, because the pipes are earthed by the boiler and so unnecessary bonding will not be detrimental to safety bonding is applied just in case.
In your case because of all the plastic the water pipes cannot be extaneous but I would still think the gas should be main bonded to the MET.

Something about gutting over 22k ohms and its okay to not bond?
230V/23kΩ - that limits fault current to 10mA.
Some think this limit should be 5mA so 46kΩ required.

I was told an r2 for both the above. Got open circuit all round which I expected can Someone clear this up please.
Have I?

Seems to be a grey area as I have asked around already.
More a grey matter area.
 
The pipe must be bonded where it enters the premises.
Because it is connected to the boiler it will be earthed but should be main bonded to the MET.


Well, it is.


Not extraneous then.


You could do that to be certain but no one is going to go to the bother.
So, normally, because the pipes are earthed by the boiler and so unnecessary bonding will not be detrimental to safety bonding is applied just in case.
In your case because of all the plastic the water pipes cannot be extaneous but I would still think the gas should be main bonded to the MET.


230V/23kΩ - that limits fault current to 10mA.
Some think this limit should be 5mA so 46kΩ required.


Have I?


More a grey matter area.

The someone I mentioned above on all reference was the niceic technical helpline. I left the conversation still needing to ask on here coz the answer I got was so minimal.

He said the gas could probably get away with not being bonded if I got a reading above 23kohm.
Of course I got open circuit.

Shall I just consider that I need to get a 10mm to the gas metre ?
 
If the gas coming into the property to the meter is plastic and the outgoing pipe does not enter the ground then you do not need to bond it. If it's a metal pipe to the meter then bond it
 