Discuss Bonding of conduit in kitchen floor in the UK Electrical Forum area at ElectriciansForums.net
Bit of a debate today, advice please as regs book not possible to get in my hands until tomorrow. New job, apartments, in the kitchen there are 2 x 25mm conduits from an external wall to an island within the kitchen that is free standing, to be able to get the hob supply across and lighting with a spare in case any sockets are added at a later date. My question is, do these require bonding? Thanks in advance.
If they are in good contact with earth(generally below the foundations) and meet the definition of an extraneous conductive part then They will require protective bonding to the MET
Have you tested the conduits to see if they are extraneous?
If the cable installed inside the conduit is insulated and sheathed such as twin&earth , then does it still need to be earthed as you effectively have double insulation unlike singles?
Insulated and sheathed is not the same as double insulation.
No it’s not but do you see were I’m coming from?
The added protection you have with twin & earth is it necessarily needed to earth the conduit?
Perhaps if buried in the floor against impact yes but otherwise I’m not convinced.
Open to discussion
Try regulation 412.1.1 double or reinforced insulation
Basic protection and fault protection are provided by reinforced insulation between live parts and accessible parts.
Regulation 412.2.
Singles don’t have reinforced insulation so understandably need containment as per regulation 521.10.1,where as twin and earth does, so I’d say it’s not necessarily a requirement to Earth the conduit if metal containing insulated and sheathed cables
Reply to Bonding of conduit in kitchen floor in the UK Electrical Forum area at ElectriciansForums.net
Hi, this is a repost of the initial in diy as the only potential diy aspect is the prep ahead of a qualified person attending, this is hopefully...
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
4K
Hi all, First post here, hope I'm compliant with the rules! I did do a quick search before asking this, but I couldn't quite come up with the...