sparkyork

hi all, just been on a job today altering a ring main in a utility room and moving the lights around a bit. was waiting for a plumber to get out me way so went for a wander round.. i then found an oil tank in the back garden with no bonding to it. water has a 10mm. consumer unit is a large mk sentry (my favourite!) so im fine for making stuff rcd etc. the board was changed january this year and i said to customer that they should of bonded the oil at least???? shall i phone them and see if they will do it!??
would fancy doing it me self but it looks a T$at to get to and customer said just leavr it!!

also not broke the seal on the fuse yet to see what raiting it is. but the tails to the board are in 16mm and main earth is 10mm, on a tn-s system. if the fuse is 60A am i right in thinking that 16mm tails and 10mm earth are ok?? but if bigger fuse then earthing is defo undersized??

comments gladly appreciated
 
Bonding to oil pipe needs doing (deep down you know it ;)), due to the size of the pipe (microbore size usually) I use a bare micc P clip & put a ring terminal on the bonding conductor, which is then nut/bolted to the P clip.

If the service cutout fuse is rated to no more than 60amp you can leave the tails as is but I would make a comment on the cert. I always change the tails to 25/16mm if doing new works such as changing cu, but for MW leave as they are.
 
im sure it says in the regs for cables up to 25mm csa ,earth should be the same size,then over 25mm it halfs,or have i dreamt it.i,e,16mm tails =16mm earth. 25mm tails =12.5mm earth but there no such animal so you got to use 16mm again.
 
not checked out above table but yeah i always thought it was kinda half the size, so 25mm tails get a 16mm earth and 16mm tails , well technically should maybe be a 16 but it is only minor works so may just make a note. i might give this company a ring and see why they didnt bond the oil service, ill do it if they wont but again if the customer dont want me to do it then..??
 

Reply to bonding to oil tanks in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi, searched but still niggling problem need help on... Installation: - 4mm earth to earthing electrode (rod) Ra 42ohm Zdb 33ohm 1361 60A main...
Replies
19
Views
3K
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
648
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
6K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
702

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock