And you know it is there and there will be information left for future occupiers or anyone who would want to disturb it. That's the way it should be done . It is all about consideration and common sense.I’ve buried some swa in ducting in my garden. Probably no more than 50mm under the ground, no yellow tape. It’s under some artificial grass or slabs, so no digging likely.
You rebelI’ve buried some swa in ducting in my garden. Probably no more than 50mm under the ground, no yellow tape. It’s under some artificial grass or slabs, so no digging likely.
I buried a body under slabs once. Think it was an objectionable, old NICEIC assessor
Depth of buried SWA cable 500mm lay in sand. cover with warning tape at higher level. You may have to make Cabin a TT installation with eath Rod
Only if House or main supply is PME
See Attached, SWA Armor sheath is earthed at main board. The earth is isolated at outbuilding and eath rod installed to form a TT system with a 30ma RCD covering outbuilding. The supply to SWA cable feeding outbuilding should be protected by a time delayed RCD 100ma
there is a lot on the web about not exporting PME.
Agreed however there are recommendations as attached document READ MORE HERE and you may need permission From DNO to export PME.