Discuss Busbar chamber in the UK Electrical Forum area at ElectriciansForums.net
S
sparky87
Hi all, Have a 200amp bus bar chamber located in a maintenance shed that feeds several isolators/ DB. This is fed from a 100 amp 3phase switch fuse located at the origin located within a different building some 70-100 meters away at high-level. Does the bus bar chamber require local isolation? I.E switch isolator on incoming cable? many thanks in advance
Like above, ideally you would have an incomming isolator as a local means, having said that as this is an existing install, if the front end Sw/F can be locked off then there isn't any real need to address the issue, anyone working on the busbar can safely isolate and lock-off the front end which would be fine in my books for an existing set-up.
Reply to Busbar chamber in the UK Electrical Forum area at ElectriciansForums.net
Evening, I've been asked to install a supply to a sprinkler system in a new installation that must be separate to the building electrical...
Incoming supply on our job comes into the building and then the tails from which go into a switched isolator with 200A fuses fitted. No idea...
Hello All, I've been tasked with adding a PV system on to a site which has a 1600A SAIF feeder pillar as its incomer. Not overly familiar with...
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...