I did an EICR and found two lights in a bedroom that are florescent lights so class 1 but the lighting circuit is old and does not have an earth. However, the lights are in vanity units, so you cannot touch the units without dismantling the vanity units. As they cannot be touched, can the C2 for using an earthed fitting on non earthed lighting circuit be downgraded to C3?
 
C2 for me because to say they cannot be touched isn't good enough, you did:)
 
The more I think about it, the more I think it has to be changed to class 2 fittings if the client wants a satisfactory result.
 
The question was if the fitting is inaccessible, can the code change to C3.

But it's not inaccessible is it ?
As Handysparks and Westward pointed out, it must be accessible enough to change lamps, and for you to determine that it is class 1 with no cpc.
 
It isn't inaccessible, you got to it. I think Class 1, no cpc, minimum Code 2.
 