Guest123
2.5mm protected by a 32A breaker, really???
Yes
Well depending on number of cores and installation method this exceeds the CCC of the cable.
It might just be me but I wouldn't entertain the idea of protecting a 2.5mm with a 32A MCB regardless of what the book says it can handle, it just doesn't sit right. 20A MCB max.