I have a rewire on an ancient farmhouse, the builder suggested running cabling on top of concrete sub floor in trunking.
On top of the concrete there will be 70mm celetex insulation and the electrical trunking will be installed within this layer.
The wet WFH system will be laid on top of this.
Anyone ever done this before???? Obviously thermal effects of the heating will need to be considered etc

Thanks in advance

G
 
I've done it with conduit before. I wouldn't use trunking because it'd be harder to draw the cables in and out.
I forget what we did about the heating; I seem to remember it wasn't a problem because it only heats the floor to about 40° or so.
 
Used conduit myself in these situations as well,but trunking could equally be used.......heating shouldn't be an issue as the cables will be insulated from it by the celotex. Obviously you will need to calculate cable sizes based on the appropriate reference method.
 
As a point of desperation you can also just bury the cable direct in concrete, there is a BGB method number for it.
 
I didn't claim it to be first choice!!
 
I did not think that you could bury cables directly in concrete du to it`s acidic properties, but i could be wrong.

You are thinking of bare copper pipe and the like. Likewise bare MICC!! Any PVC covered cable wouldn't be affected by acidic, sulphates and chlorides that may be found in concrete and cements etc...
 