Called out to rental property i carried out an EICR on in March; this year to look at loss of power.
Narrowed it down to the down stairs ring main, done end to ends and ring in tact, insulation resistance failed, dropped every socket and inspected the wiring and socket fronts which 2 i had to replace.
Split the ring and worked on each leg and found it to be the return leg from the last socket; checked the EICR test results and it was over 200m ohm then; tenant swears there's been no DIY taken place but bar a rodent eating the cable or physical damage i.e a screw or nail im at a bit loss to how its gone from 200m ohm to failure.
Ended up downgrading the MCB to B16 and informing the LL the sockets need rewired asap as the leg on the B16 is on 2m ohm, genuinely think he thinks im trying to rob him!
anyone similar experiences?
 
Would 2M Ohm trip the RCD though?

PS, not being picky but use upper case M to avoid confusion, unless you do mean milliohms.
 
no that is the connected leg 2 M ohm, the disconnected leg at the CU and last socket has the complete failure on.

That seems odd then. If the ring last time was 200M, and now both legs are significantly lower. Two faults? Or 2 bits of DIY 😀
 
Called out to rental property i carried out an EICR on in March; this year to look at loss of power.
Narrowed it down to the down stairs ring main, done end to ends and ring in tact, insulation resistance failed, dropped every socket and inspected the wiring and socket fronts which 2 i had to replace.
Split the ring and worked on each leg and found it to be the return leg from the last socket; checked the EICR test results and it was over 200m ohm then; tenant swears there's been no DIY taken place but bar a rodent eating the cable or physical damage i.e a screw or nail im at a bit loss to how its gone from 200m ohm to failure.
Ended up downgrading the MCB to B16 and informing the LL the sockets need rewired asap as the leg on the B16 is on 2m ohm, genuinely think he thinks im trying to rob him!
anyone similar experiences?
Many times. A near-fault can sit there for years before it decides to become an actual fault.

An interesting example is one I visited a couple of weeks ago. The kitchen ring final was tripping, both the MCB and the RCD. Sometimes sporadically, sometimes every time the circuit was energised. The actual fault was due to 4 cables being forced into a 25mm steel backbox housing a FCU for the cooker hood. Eventually one of the line conductors had become damaged and was arcing to the top lug of the backbox.

Interesting because it hadn't been worked on for years, but also because at no point during my testing did I get a low IR reading L+N to E. With both MCB and RCD tripping with a noisy 'pop' on energising, you'd expect a dead short L to E, but I was getting >60M Ohms at 500V. Very strange.

BTW, 2 M ohm isn't that low, and is IME a common result for when equipment is still plugged in
 
Socket face suddenly failed?

I had that a couple years ago at Xmas eve for a neighbour… individual legs between sockets were fine, but as I replaced the fronts, IR on L-E dropped like a stone.
Suspect splashed liquid as faulty socket was in kitchen.

WAGOed through joint, faulty socket as makeshift blank plate until wholesalers were open again to get a replacement.
 

Reply to call out to ring main fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
793
Hi all, I have been on a site repairing damage caused by travellers collecting copper for the last week. We have found and replaced cabling to get...
Replies
17
Views
3K
Hi all , after some opinions on N-E fault or ring main. After chasing this fault and ruining my bank holiday weekend , ring main IR readings as...
Replies
3
Views
1K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
780

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock