Called out to rental property i carried out an EICR on in March; this year to look at loss of power.
Narrowed it down to the down stairs ring main, done end to ends and ring in tact, insulation resistance failed, dropped every socket and inspected the wiring and socket fronts which 2 i had to replace.
Split the ring and worked on each leg and found it to be the return leg from the last socket; checked the EICR test results and it was over 200m ohm then; tenant swears there's been no DIY taken place but bar a rodent eating the cable or physical damage i.e a screw or nail im at a bit loss to how its gone from 200m ohm to failure.
Ended up downgrading the MCB to B16 and informing the LL the sockets need rewired asap as the leg on the B16 is on 2m ohm, genuinely think he thinks im trying to rob him!
anyone similar experiences?
Narrowed it down to the down stairs ring main, done end to ends and ring in tact, insulation resistance failed, dropped every socket and inspected the wiring and socket fronts which 2 i had to replace.
Split the ring and worked on each leg and found it to be the return leg from the last socket; checked the EICR test results and it was over 200m ohm then; tenant swears there's been no DIY taken place but bar a rodent eating the cable or physical damage i.e a screw or nail im at a bit loss to how its gone from 200m ohm to failure.