it's my own house so not realy needed but as i would of put an isolator in anyway 20 quid for rcd doesn't seem to much effort.
edit missus house she would kill me if she heard me calling it mine!
 
main incommer from meter goes to isolator then into henley block on distrubution board then split from henley to cu's on the board,the new supply to top flat will come from this henley to rcd on board then swa tails into ceiling metal box then on to top flat cu.
does this make better sense ?

What's the overcurrent protection for the new SWA submain?
 
What's the overcurrent protection for the new SWA submain?

I was thinking the same as HandySparks here. In reality you are extending the tails (up to the flat) beyond the usual allowance of 2 metres. You'll need to sub fuse the supply for the flat. If your main cutout is 100amp, you can use one of those MEM switchfuses fused at 80 Amp.

Pete
 
Do you need to put further overcurrent protection on the tails? Isn't that what the DNO fuse is for?

Earthed conduit with normal tails would be easier than SWA wouldn't it?
 
I got lost on post 1 .... read all through and still lost..

Here's what i think he needs to do....

Metal clad sw/f unit fed by tails off origin
Swa up to flat , if needed to be joint then metal clad box with earth tail linking banjo's, crimp and heat shrink sleeving (no-one want to see a box lid in the ceiling, poor workmanship when you are at the design stage).
Swa is not required to afford rcd protection and this can be ne in the flat CU...
If you are fitting a fused isolator remember the installation should require 1 point of isolation so take this into account.
 
Solid conductors should NOT be crimped. Fact.
Should not or Must not?
There are suitable variants of crimp types for solid conductors especially in the RF industry other wise the likes of Molex, Huber-Suhner Radiall etc would not use them themselves.

Where has the mention of solid conductors come from?
25mm CSA armoured cable and singles used for tails are made up of more than one strand!

So maybe you could have said, "in my opinion low and high voltage cables must not be crimped due to thermal effects etc, etc..."
:rolleyes:

- - - Updated - - -

this is far far from fact

Fact!!
 
Fact is I'm very lost with this thread. Gone from suspended ceiling to plaster ceiling with trap. Gone from 80 a 30ma to 100ma .Gone from his house to his misses house. Gone from rcd to switch fuse isolator. Can some one pm me when he finished and tell me what he does. Lol :lol:
 
Fact is I'm very lost with this thread. Gone from suspended ceiling to plaster ceiling with trap. Gone from 80 a 30ma to 100ma .Gone from his house to his misses house. Gone from rcd to switch fuse isolator. Can some one pm me when he finished and tell me what he does. Lol :lol:

You missed out that there is also time delay,so expect that pm to be late as well
icon7.png
 
My eyes must of fully shut by that point, :drunk::drunk::drunk:

- - - Updated - - -

My eyes must of fully shut by that point, :drunk::drunk::drunk:
 