I have checked the regs and can't find anything to say this can't be done. Although I'm worried about cable movement in the case of short circuit damaging singles in the trunking
 
You are fine with that. Of course usual good installation practice needed, but SWA won't move that much unless you are looking at really high energy faults, and more so for sets of AWA singles making up a really high current 3P set.
 
do you mean complete SWA? with the armour? or glanded into the trunking, and the inner cores within trunking?


"Singles" cable has a slightly tougher insulation than something like the inner basic insulation of t&e... Can take a bit of rough treatment no problem.
 
do you mean complete SWA? with the armour? or glanded into the trunking, and the inner cores within trunking?


"Singles" cable has a slightly tougher insulation than something like the inner basic insulation of t&e... Can take a bit of rough treatment no problem.
Yes, complete SWA. We have installed trunking for an installation with 2.5mm, 4mm and 6 mm singles.

We've now been asked to run a 10mm swa for a supply to a new dB and a lot of the trunking is along this route.
 
You are fine with that. Of course usual good installation practice needed, but SWA won't move that much unless you are looking at really high energy faults, and more so for sets of AWA singles making up a really high current 3P set.
Thanks for the reply, the fault current will be 10Ka (theoretical maximum at origin) for the swa as we are right by the site intake.

We have at a maximum 10 single conductors (2.5, 4 and 6mm) at the busiest points in the trunking. All single phase including SWA. I suggested it to the clerk of works and he said absolutely not allowed.

I disagreed and have since been searching high and low for a regulation that prohibits this.
 
I can think of reasons why the clerk of works might not want SWA eating up space in trunking, but none that involve wiring regulations.
 
Possible future plans require the space in the trunking?

Whats wrong with running the SWA alongside the trunking? Its mechanically protected already. Or, as i said earlier, gland it in and run it through without the armour.
 
Clerk of works will have the final say. I wouldn't waste time arguing with him and would instead ask how he'd like it to be routed - limitations with regard to support might actually result in him having a change of mind. Do whatever he wants and invoice accordingly.
 
Possible future plans require the space in the trunking?

Whats wrong with running the SWA alongside the trunking? Its mechanically protected already. Or, as i said earlier, gland it in and run it through without the armour.
For some reason he doesn't like it clipped direct. Unfortunately it's at the beginning of a 70m run so glanding into trunk is not an option. Clerk also refuses to allow us to clip direct.

I was only really looking for 2nd opinions on this matter as he has highlighted my suggestion to run in the trunking to the client and has questioned my competency
 
Clerk of works will have the final say. I wouldn't waste time arguing with him and would instead ask how he'd like it to be routed - limitations with regard to support might actually result in him having a change of mind. Do whatever he wants and invoice accordingly.
He has refused to make suggestions on how to actually do it as he states 'that's not his job'.

I wanted to triple check that this is in fact acceptable as he has reported my suggestion to his superiors.

Thank you for taking the time to reply!
 
Just one other thought, how would the SWA armour be connected?
I can see both sides of this, whilst I also cannot see a reason why it is Non compliant, it will take up more room in the trunking than the equivalent in singles?!
Personally I would if in trunking be using singles for ease and space saving.
When they ask you back again at a later date to install more circuits you will either be wishing for more space or thinking, glad I left some spare capacity in that trunking!
Just my 2pennies worth.
Sy
 
He has refused to make suggestions on how to actually do it as he states 'that's not his job'.

You've suggested two methods of installation which he has rejected and neither for any regulatory reason and this is something I'd make very clear to him - I'd contend that it's very much his job to decide how the cable is run, unless the client provides a spec.
 
Is it not possible to use singles in trunking. Sounds like he for some reason has an issue with you and will find a problem no matter what you suggest.
 
If I had more than one run of SWA I would be tempted to put up cable tray and clip to that. If the tray is vertical (parallel to wall, supported off by short lengths of strut, for example) then you need the occasional metal tie for fire support in addition to regular ties of any other sort.

If the SWA sits on top of a horizontal tray (so it can't fall if clips melt), for example supported on cantilever arms, or suspended from a roof, then standard cable ties are OK. Personally I would always use the black UV-tolerant type even indoors as sometimes it will get sunlight from windows, etc, and it saves me keeping multiple bags.

However, I also get the feeling this person is being difficult for no obvious reason. I would be tempted to present your suggestions for alternatives in writing (e.g. email) and make sure they respond also in writing just to cover yourself.

Incidentally, when you said trunking I was thinking of the metal stuff, 50x50mm upwards, not plastic. Can you confirm the type?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Can SWA be run in the same metal trunking as singles?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
43

Advert

Thread statistics

Created
twilks,
Last reply from
Mike Johnson,
Replies
43
Views
5,164

Advert

Back
Top