i=p/u

Think I'm wiring lam posts this week , is there any info in the regs, or is it not there and just apply common rules/ principles.
 
Your going to hate me...lol B5489 design and installation of street lighting....only applies really if it in a public envoiroment
 
Well I briefly remember from before the cover was linked to post... Then a flex right upto fitting...

Isnt 4mm sufficient
 
6mm is the standard post earthing conductor size requested by most L.A's.
and there is a section in the regs that covers street furniture and highways supplies but makes dull reading.
 
Make sure you have spare tools and materials because you always end up dropping something down the hole.
 
The door/hatch must always face away from on coming traffic so that when you are working on it you can see the cars coming towards you.
 
Is there a sum/equation to determine. Size. 10A braker. But I'd say 4mm is sufficient as needs to be protected otherwise. And it's same size as conductors ...
 
Anyone ever fit them lucys? I'm sure yes. . They are wired in 4core using swa as earth. And it's labeled at bottom half L1,L2,N,L3 but the fuse can only go in L1 so need to change conductors about and effectively they ain't labeled right then. . So If drawing says this light is L3 it's the grey that is going into L 1 if you know what mean... Pfffft
 
street lighting crash course.........

50w / 70w / 100w lanterns = 1.5mm Cable & 6A fuse
150w / 250w / 400w lanterns = 2.5mm cable & 10A fuse

yes , rotate phase conductors to the cut-outs fused terminal to match the phase allocated to each lampost , which will almost certainly begin Br - Bk - Gy , etc.

fit earth block & earth label on back board above cut-out and run seperate 6mm earth straps to post , door & cable fixing plate , using ring crimps and 8mm nuts/bolts.
 