My son, who was banished to one over the winter of 2020-21, as a Covid precaution, would probably strongly disagree.
The 2kW heater in mine is only described as an auxiliary to the gas heater, which has an output of over 3kW.
You should close the windows then, or get a van that's insulated.
 
Selectivity is always going to be a problem with having two 30ma rcds one at the hook up point and one in the van, even if using 100ma S type or similar at the source.
True, but what goes on in the caravan is out of our control. Regs say we have to provide RCD protection for the socket.
 
Can't have an S type for the 16A socket. There's no guarantee that the 'van has any kind of RCD, or it might be just a 13A extension lead to a tent plugged in.
 
As Pretty Mouth says, we have no control over the van's installation, and the van owner has no control over what he plugs into.
Another potential problem that's beginning to appear, is that Motorhomes (often DIY made) often have petrol invertor generators built in, and who knows what the changeover arrangements are for them.
 
Can't have an S type for the 16A socket. There's no guarantee that the 'van has any kind of RCD, or it might be just a 13A extension lead to a tent plugged in.
I said at the source 30ma at the hookup.
As Pretty Mouth says, we have no control over the van's installation, and the van owner has no control over what he plugs into.
Another potential problem that's beginning to appear, is that Motorhomes (often DIY made) often have petrol invertor generators built in, and who knows what the changeover arrangements are for them.
As you have just said, “no control over the vans installation”. So not a problem.
 
What's the point if the supply cable is SWA? No harm, but little point either, since there already should be two 30mA RCDs between the source and the customer.
I assume its pme you may not get the disconnection time.
 
Electrocuting innocent caravanners is NOT good for business.
If the RCD at source is needed to meet disconnection times in the event of a cable fault, then fine. That's all down to design.
 
Electrocuting innocent caravanners is NOT good for business.
If the RCD at source is needed to meet disconnection times in the event of a cable fault, then fine. That's all down to design.

Ok so are you saying that the OP needs to install into the design a circuit that detects flow into the source ?.

Maybe have some sort of sprinkler system as well as a fire alarm and security just in case they have fire arms
 