- Reaction score
- 8,777
Could you consider using fuses upstream?But for upper limits, B16 is 5X16=80A, vs C10 10X10 =100A. I can see selectivity with the upstream device being an issue if I use C10s?
Discuss Caravan diversity question in the UK Electrical Forum area at ElectriciansForums.net
Could you consider using fuses upstream?But for upper limits, B16 is 5X16=80A, vs C10 10X10 =100A. I can see selectivity with the upstream device being an issue if I use C10s?
Why do you need a double outlet ?These are supplied at the hookup unit.
I'm fairly happy with the regs side of the job, I'm just trying to fathom whether I treat the circuit feeding the hookup unit as a 32A load, or if I can apply some diversity to it
Yes, I guess....Could you consider using fuses upstream?
As @brianmoooore said, it's 2 pitches, side by sideWhy do you need a double outlet ?
All the touring hook up sites i have seen have been single outlets with 30ma rcd and 16amp mcb.
Rolec 1 Way 16A Caravan / Campsite Hook Up Point Box (LSAA0010) | Electrical Discounted Supplies
Rolec 1 Way 16A Caravan / Campsite Hook Up Point Box (LSAA0010) from Zetmet Ltd discount electrical supplies.electricaldiscountedsupplies.com
Also, all the Consumer units in the caravans / motorhomes i have seen has a 16 / 6amp MCBs and 30ma rcd.
Is there likely going to be other hook-ups in the future ?As @brianmoooore said, it's 2 pitches, side by side
My son, who was banished to one over the winter of 2020-21, as a Covid precaution, would probably strongly disagree.a 2kw heater in a van will warm the van up in a minute or two.
Selectivity is always going to be a problem with having two 30ma rcds one at the hook up point and one in the van, even if using 100ma S type or similar at the source.Is there likely going to be other hook-ups in the future ?
Most caravans know not to draw too much, and a 2kw heater in a van will warm the van up in a minute or two.
The customer doesn't think there will beIs there likely going to be other hook-ups in the future ?
Most caravans know not to draw too much, and a 2kw heater in a van will warm the van up in a minute or two.
As we all know, the customer doesn't usually have a clue.The customer doesn't think there will be
You should close the windows then, or get a van that's insulated.My son, who was banished to one over the winter of 2020-21, as a Covid precaution, would probably strongly disagree.
The 2kW heater in mine is only described as an auxiliary to the gas heater, which has an output of over 3kW.
True, but what goes on in the caravan is out of our control. Regs say we have to provide RCD protection for the socket.Selectivity is always going to be a problem with having two 30ma rcds one at the hook up point and one in the van, even if using 100ma S type or similar at the source.
True, but what goes on in the caravan is out of our control. Regs say we have to provide RCD protection for the socket.
Its still selectivity.Selectivity between the caravan RCD and the hook up point RCD isn't important. Selectivity between the hook up point nd the source of the power is.
I said at the source 30ma at the hookup.Can't have an S type for the 16A socket. There's no guarantee that the 'van has any kind of RCD, or it might be just a 13A extension lead to a tent plugged in.
Selectivity is always going to be a problem with having two 30ma rcds one at the hook up point and one in the van, even if using 100ma S type or similar at the source.
What's the point if the supply cable is SWA? No harm, but little point either, since there already should be two 30mA RCDs between the source and the customer.I said at the source 30ma at the hookup.
I said at the source 30ma at the hookup.Can't have an S type for the 16A socket. There's no guarantee that the 'van has any kind of RCD, or it might be just a 13A extension lead to a tent plugged in.
As you have just said, “no control over the vans installation”. So not a problem.As Pretty Mouth says, we have no control over the van's installation, and the van owner has no control over what he plugs into.
Another potential problem that's beginning to appear, is that Motorhomes (often DIY made) often have petrol invertor generators built in, and who knows what the changeover arrangements are for them.
Reply to Caravan diversity question in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.