Engineer54
Personally I wouldn't use isolated rods at each hookup.
I'd be looking to create one large earth nest to give the lowest most stable Ra possible, possibly installing rods at each hookup but having them all linked together.
I know it would technically be a departure but I see no issue with having an earth nest of very low Ra connected to the MET and having the PME connected.
That would be by far the best solution.
Why would you call it a departure?? All you are doing is providing an addition local N-E to the PME supply earth system. In this instance though, the Ra of the earth nest needs to be below 10 ohms, which isn't a very difficult task if you are installing a earth nest!!