A glance at page 21 indicates the 3 phase version of the charger requires three lines and a neutral as you have already spotted which your home does not have. But even if you had a 3 phase 4 wire supply, the line to line voltage for the charger needs to be 380V +/- 10% and your home only has 230V (IIRC) between L1-L2, L1-N and L2-N.


You may wish to add up what power is supplied by each of the pairs L1-N, L2-N and L1-L2 in your home at different times of the day. And then look at the sizes of the cutout fuses in the L1 and L2 incoming lines to determine what your maximum power demand can be. A fuse should not be operated long term at its rated current - derate by 0.75.

A single phase 11kW charger is circa 11000/230 = about 50A.

Ask again if you are not sure.
There are no fuses here.
But I've gone for the single phase 7kw charger. (looks like it is adjustable also so can set it to charge at less than 7)
I have 15kw supply to my house.
Only time it will be close to the max is when I have a lot of the underfloor heating on in the winter between 4am-7am.
Just need to be aware of the times this comes on (only for 2-3 months of the year too).

Thanks
 
There are no fuses here.
But I've gone for the single phase 7kw charger. (looks like it is adjustable also so can set it to charge at less than 7)
I have 15kw supply to my house.
Only time it will be close to the max is when I have a lot of the underfloor heating on in the winter between 4am-7am.
Just need to be aware of the times this comes on (only for 2-3 months of the year too).

Thanks
You do not have fuses acting as automatic disconnection of mains supply but you do have this three pole circuit breaker somewhere near the meter if I remember correctly. It is rated at 40A.
 

Attachments

  • _attachments_thumbnail10-jpg.57674_.jpeg
    _attachments_thumbnail10-jpg.57674_.jpeg
    184.6 KB · Views: 2
You do not have fuses acting as automatic disconnection of mains supply but you do have this three pole circuit breaker somewhere near the meter if I remember correctly. It is rated at 40A.
They upgraded it last year to 63
Also the wall charger (arrived today) comes with built in type B 30mA AC and 6mA DC approved unit by UTE
My English speaking electrician (Electrical engineering degree from university St.Petersburg Russia - new expat here) recommended also to add a Connex 2P 40A 30mA serie RCCB curve C - CN1040
and 32a circuit breaker. Both ordered with a IP66 enclosure. to go next to the wall charger.

Main breaker next to the meter:

1764781199784.png
 