If the other heater is working through the night ,and both heaters a supplied from the same board, then the supply to the board is ok.
Has anyone checked the fuse in the board. (fuse box)

If the Dimplex lads had it working , it has to be a fault in the supply circuit.

Thanks, the fuse board fuse must surely be ok if the second Sh is working?
Yes it seems that a fault in the supply circuit could be the culprit.
 
Thanks, the fuse board fuse must surely be ok if the second Sh is working?
Yes it seems that a fault in the supply circuit could be the culprit.
No, they are usually on separate fuses.
Also they are usually switched by a double pole switch and not a fused connection unit.
 
If the other heater is working through the night ,and both heaters a supplied from the same board, then the supply to the board is ok.
Has anyone checked the fuse in the board. (fuse box)

If the Dimplex lads had it working , it has to be a fault in the supply circuit.

This is a pic of the board, my fuse board is the one on the left, it has 3 fuses, one for the ceiling lights, one for the sockets, the other must be the night supply the heaters.


IMG_9408.jpg
 

Attachments

  • IMG_9408.jpg
    IMG_9408.jpg
    205.3 KB · Views: 131
The fuse box on the right is the one on off peak.
If you think the blue 15a mcb on the left board is controlling your storage heater it is not on off peak.
All breakers are set anyway , if the mcb is ok the supply is faulty or the Dimplex lads were wrong about the heater working supplied direct . (unlikely)
You need to get an Electrician to look at it for you, it seems it is a supply fault.
I have not deciphered all those cables , but that is the gist.
 
If your electrician were to open up the off-peak distribution board (after isolating), he (or she) would be able to identify the heater you are having a problem with, measuring the resistance (of the heating element - L to N), and being able to see it turned on/off at the local control or isolating switch. That would confirm the circuit is OK (or not). Your electrician should be able to do this without having to have this explained.

I have on occasion found a storage heater that has a faulty thermostat, so it turns off after a small amount of heat input, but unlikely in this case since it is new.
 
Last edited:
One thing you could do, having seen this photo, is to take a reading each morning of the "low" reading - this should show if off peak power is being used and how much.
 
The metering seems a tad strange to me. Is there any way you could post another picture, but with the pale blue label under the meter held up out of the way? The right hand Actaris meter seems to be fed from the load side of the E7 meter, while there are two 2.5mm T&cpcs running between the Actaris OP meter and your OP board, which is also fed from the teleswitch. If I could see the underside of the E7 meter, I might get a better idea.
 
is the room temperature actually dropping low enough at night to trigger the thermostat into switching the heater on,can you hear the thermostat click when you turn it,ive had callouts like this before with the thermostat set for about 15 degrees and a room temp of about 18 degrees so it never came on
 
Looks like someone has done a bit of a bodged job and installed a check meter to monitor the usage from another heater somewhere else in the building and done a bit of a thru crimped connection inside the off peak db
 
Last edited by a moderator:
Yes , as I understand it, he only has two heaters. The third fed from his board to.., or the fuse redundant.
I could not be bothered to try and decipher the cables lol.
 
Last edited by a moderator: