The metering seems a tad strange to me. Is there any way you could post another picture, but with the pale blue label under the meter held up out of the way? The right hand Actaris meter seems to be fed from the load side of the E7 meter, while there are two 2.5mm T&cpcs running between the Actaris OP meter and your OP board, which is also fed from the teleswitch. If I could see the underside of the E7 meter, I might get a better idea.

It looks to me like the sub meters are being used to bill a second rented out unit without going to the trouble of a second supply.
So both meters are connected after the DNO meter. The 24hr one Feeds the KMF and then the off peak one is connected to the outgoing way of one of that boards circuits, the other T&E being jointed to the original outgoing circuit
 
This is all sorted now, the sparks came back and checked the night supply fuse & supply cable route, both fine, he then connected the SH with a temp lead again and it heated up. As a last resort he removed the fused was outlet, when he tested it it started to transfer current then stopped, he notice a hairline crack in it. He put a new one on and the heater works fine. Strange as there was no sign of the wall outlet heating up or anything. Thanks to all your inputs
 