Gas bonded with 10mm at front of flat, boiler at back of flat where a 6mm has been linked from it to an extraneous cold water pipe in bathroom.

No other extraneous water pipes in flat.

All continuity good but using the gas pipe as a conductor to link to water pipe.

C3 for 6mm
C3 for non continous bond

Is there a code for using the gas pipe as a link/conductor to the water pipe?

Cheers
 
543.2.3 a gas pipe shall not be selected as a protective conductor.

I would code this C2, as the water bonding is relying on the use of the gas pipe, and should have its own protective bonding conductor.

There is no requirement for continuous bonding.
 
Continuous bonding used to be quite common on new build flats where we would take a 10mm to the gas or water then link across to the other...
always seemed a bit lazy to me but I was just a su by so did what the main contractors told me to do...
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Code for bonding?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
4

Thread Tags

Advert

Thread statistics

Created
Bailey326,
Last reply from
Dustydazzler,
Replies
4
Views
3,424

Advert

Back
Top