I'm getting in a bit of a muddle as to whether this is a code C3 or no code.

This is an EICR. The CU has a 100mA main switch. The lights have 100mA protection the rest of the install has 30mA protection. It is a TT.

The Best practice guide clearly says no RCD protection in this scenario is a C3, but it doesn't state if this has to be 30mA.

Cheers all.

Ps.. also reg 701.411.3.3 clearly says 30mA needed.
 
Last edited:
411.5.2 says a RCD doesnt need to be fitted, but is preferred.
701.411.3.3 is for rooms containing a bath or shower, so you have one or more of those in the property?

Edit are any cables buried in walls?
 
Plenty of cables buried in walls.

Yes, it does it serve a bathroom and there is supplementary bonding in place.
 