hi all , i have been having a debate about which mcbs should be used in a distribution board.
I understand the the pfc should be lower than the appropriate device (6k or 10k).
6k is usually single phase domestic distribution boards and 10k is 3 phase commercial.
I understand that if the mcbs are different manufactrures they can be either a c3 0r c2 depending on situation.
My question is if a 6k is fitted to a commercial board which is usually 10k , would there be any coding when carring out an EICR if the pfc is lower.
Again would you code if any ..
These would be the same manufacture.
I was always led to believe it was to be as per manufactures instructions. which would recommend 6k in domestic and 10k in commercial.
thanks
mark
 
Provided they are compatible with the enclosure and the line to line PFC is not likely to exceed 6KA I don't consider it as an issue. Manufacturers may have differing opinions on this however.
 
From memory, it's not as simple as that.

I recall, on a different forum, there being some debate about what the regs actually require, so I went and looked at the BS that covers distribution boards - the interest was in "domestic CUs", and people were saying things like "must have a self closing flap on the front" (false), "must keep any fire inside it" (false), and a few others.
One of the things I found was that the devices are not actually required to break the full prospective short circuit current - simply because the standard assumes the presence of the upstream DNO (or submain) fuse which will itself limit the let through energy. Again from memory, it was something like the assembly is tested with a 16kA fault current, but the MCBs can be rated at only 6kA or 10kA provided they will withstand the 16kA until the upstream fuse ruptures.

Once you go past the single phase 100A domestic CU, then a different bit of the standard applies, but I suspect the same considerations apply - and the allowable MCBs will depend to some extent on the upstream protection and it's tripping characteristics. But that's well outside of my comfort zone.
 
The short circuit rating of the downstream device is determined by the energy let through of the upstream device under fault conditions.
The energy let through of the upstream device will depend on the actual fault level of the system to which it is attached.
 