Hello,

I bought a new build and noticed the upstairs MCB is controlling some sockets on the opposite floor, so if I flick the upstairs MCB it's also switching off a socket downstairs (I think it's a spur) in addition to all the ones upstairs

Is there anything within 7671 that states this is wrong?

I asked the contactor on site and they said it can be re-wired but it's down to my prefrence. Is this correct? Surely the regs have something to say on this.

P.S this same contractor didn't earth some of the metal faceplate light switches (including backbox) - so I don't trust them at all. Despite having a NIC form filled in and signed by two qualifed electricans!!
 
Last edited:
Nothing wrong with having sockets on different floors wired on the same MCB as long as the labelling on the CU reflects this or doesn't mention 'upstairs' or 'downstairs' at all.
I've almost always grouped socket circuits in downstairs rooms with the rooms directly above, except for kitchens and utility rooms.
 
Nothing wrong with having sockets on different floors wired on the same MCB as long as the labelling on the CU reflects this or doesn't mention 'upstairs' or 'downstairs' at all.
I've almost always grouped socket circuits in downstairs rooms with the rooms directly above, except for kitchens and utility rooms.
Hi nope it has stickers for upstairs and downstairs
 
It is an odd thing to do but nothing wrong with it, might gave been done if the other circuit failed you still have one close by working. Metal switch front plates not being earthed is a big issue.
 
They should both be earthed. I wonder if the other properties are the same, this sort of thing is fundamental.
I asked that question but they wouldn't answer!! It would open a can of worms regarding rework!

Our house was probably the 15th built on site so if they got this far and are making mistakes like that - it does make you wonder
 
They should both be earthed. I wonder if the other properties are the same, this sort of thing is fundamental.
I always fit a fly lead on both switches and sockets, but the last time I looked it was apparently considered acceptable to earth the plate and rely on the fixing screws to earth the box, provided one of the fixings in the box is 'fixed' and not the adjustable (to level the fitting) type.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Manchester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Comsumer unit - upstairs/downstairs ring mains
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
31
Unsolved
--

Advert

Thread statistics

Created
taconite1,
Last reply from
pirate,
Replies
31
Views
3,329

Advert

Back
Top