You don't need an EICR to sell a house. If the buyer wants one it is up to him/her to commission it just like any other surveys required.

Your right of course. But having sold my house recently, you fill in a questionaire. It’s some sort of legal document which you sign. One of the questions it asks, is are their any EICR’s etc available for the property.
 
You don't need an EICR to sell a house. However if a defective EICR comes up in the mix it can be a major headache sorting it out. Depends on who is do the conveyancing. Last house I sold the solicitors for the buyer were insanely obsessed with the conservatory asking two pages of questions about it's compliance and planning and Fensa guarantee and on and on it went it was a pain. Just saying a new EICR will cover it in this particular case.
 
Thanks for all your replies, I appreciate it. On Risteard's prompt, I went back and checked the date recommended for next inspection and it was 1 and a half years ago, i.e. 3 years after the date of the report. Now I don't know if that was auto generated by software based on the presence of a C1 or whether it was because the house and therefore the installation would be 30 years old at that date, as I understand normal recommendations are at least every 10 years. There are also other anomalies on the report that I've now noticed such as section D states that it is a 'limited condition report' but does not say what the limitations are.
So I've decided just to get another one done soon for my peace of mind. I know that legally it's not required when you sell your house but I think most buyers expect it now just as they expect the gas appliances to have been serviced. As a buyer myself, I think it's a reasonable expectation for safety reasons.
 
From what you are saying I wouldn't have too much faith in the old Report so it would be wise to get another one done.
 
Is the circuit protected by a 30mA RCD ? If the answer is yes then the results are pretty un-inportant. Maximum Zs is 1666 ohms. In practise a reading over 200 ohms woukd be considered unstable. Sorry if I've confused things. By the way if it has no 30mA RCD protection then that would be more of a concern.
 
Is the circuit protected by a 30mA RCD ? If the answer is yes then the results are pretty un-inportant. Maximum Zs is 1666 ohms. In practise a reading over 200 ohms woukd be considered unstable. Sorry if I've confused things. By the way if it has no 30mA RCD protection then that would be more of a concern.
There is an RCD in the Consumer Unit (see pic). I'm assuming it's protecting the 5 circuits to the left of it but not the 2 lighting circuits to the right?
IMG_20190303_145827840.jpg
 
Another electrician who cannot spell immersion heater but yes you are correct.
 
Another electrician who cannot spell immersion heater but yes you are correct.
I guess now you know I haven't tested it recently as otherwise I would have known! As for the immersion heater, there isn't one...but presumably there was at some time. I believe that circuit is just for the shower pump (which has also now gone so I could probably just turn that one off).
 
By pressing the button on an RCD all you are doing is checking the mechanics of the unit, not the electrical/electronics.

This crops up frequently and I believe is an incorrect statement.

If you look at the circuit diagrams for RCDs, the test button introduces a resistor connected between the load side line and supply side neutral to create an imbalance akin to that which it is designed to detect. This is why the test button is non-operational when the power is off, it requires power to create the imbalance rather than simply triggering the release mechanism.
 
This crops up frequently and I believe is an incorrect statement.

If you look at the circuit diagrams for RCDs, the test button introduces a resistor connected between the load side line and supply side neutral to create an imbalance akin to that which it is designed to detect. This is why the test button is non-operational when the power is off, it requires power to create the imbalance rather than simply triggering the release mechanism.
Does pressing the test button prove that the RCD trips within the prescribed parameters? No, all it does is prove the mechanism works, if it were to trip under fault conditions, testing it by pressing the test button will only prove the mechanics are clear of debris.
 
Does pressing the test button prove that the RCD trips within the prescribed parameters? No, all it does is prove the mechanism works, if it were to trip under fault conditions, testing it by pressing the test button will only prove the mechanics are clear of debris.

I didn't claim it did, I was merely pointing out that the test button is far from a purely mechanical test as suggested by your post to which I was replying.

It's not just you that has said this. As I said, the statement 'it's a mechanical test only' or words to that effect crops up from time to time and it is factually incorrect because it is not a purely mechanical test. The test button verifies the operation of the detection and trigger electronics, whether that operation falls within the parameters we consider to be acceptable is another matter, but none the less, if the test button works, the RCD is detecting an imbalance greater than or equal to it's rated trip current and is tripping.
 