As you already have 6mm installed use that (as you said) then use 2.5mm for the additional sockets
20A MCB is fine for protection
One advantage is you will have a very good Zs reading
I think 6.0mm and 2.5mm in the same terminal is more likely to result in an unsound connection than two (6mm or otherwise) conductors of the same CSA,as there is a risk that the smaller CSA wire will not be clamped once the screw is on the 6mm.
Just to clarify I dont believe a 6.0mm radial for the scenario the OP has described is ever a good idea...the point I was making is that despite what others have said it IS possible to satisfactorily terminate two 6mm conductors in a quality socket with a 35mm minimum back box.If you cant do it dont blame the gear.