Good idea by murdoch actually, must be early, I should have suggested that LOL
Bolt Horse Pete, see post 29, Merry Christmas by the way fella :carolers:Why not install a small CU and run 2.5mm to the sockets
2 X 6mm T&E into single sockets? Totally bonkers!!
Did we have to do a bit of pruning to get them in there? :ears:
You may get 2 X 6mm2 conductors into the terminals, but how will you get the single socket back against the pattrice LOLThat maybe bonkers but toatly possible MK sockets will accept 2x 6mm no problems. I also used single sockets so each machine has it's own socket so 2 plug tops are not connected to one Double socket
With you there, that would be a bad design and a bodge up, thats why I sugessted one twin socket rather than 2 singles so only one 6mm2 conductor is needed, that said after seeing murdochs reply I am now on the side of a small DBWell I'll take your word for it, however I still hope I never come across 2 x 6mm in the back of a socket! Ugh and on a 25mm box as well, no ta!
I am not suggesting it cannot be achieved, I am suggesting it is a silly way to make an appliance work under the circumstances mentioned in the OP, the design is poor.You can use a 35mm deep box no problems and what exactly is wrong with having a 6mm radial instead of a 4mm or even 2.5mm
As long as you terminate the cable correctly and dress the cables back there's no problem
I am not suggesting it cannot be achieved, I am suggesting it is a silly way to make an appliance work under the circumstances mentioned in the OP, the design is poor.
Totally over engineered. A 4 way Dist board would be the way forward, 2 x 2.5mm2 radials for the 2 single sockets and there would be a spare way for the future shed supply, anyhow merry christmas GazWe will have to agree to disagree there
Yes if you were desining it from start you would install a 2.5 or at a push 4mm radial
But as long as the installation was carryed out correctly there's nothing wrong with a 6mm radial
If anything it's belt and braces over engineered
As already said you can get a twin terminal socket for each conductor. If not go for the MK single termination socket. I've got 2 lots of 6mm in before without giving them a hair cut lol. Below is the MK tech spec for a singe termination socket.....
Terminal capacity:
Live, neutral & earth
3 x 2.5mm2
3 x 4mm2
2 x 6mm2 (stranded)
I'd be tempted to put in a sub db so when the client changes their mind about the shed you can add it on easily!
Thanks Murdoch, this is the obvious and best solution and still keeping a supply for the shed if needed later. The post got off to a bad start but the end result was worth the sla££ing off I got.