just got to make sure the cable end is freshly stripped and not mashed to heck otherwise your on a hiding to nothing
 
Done exactly that before, existing 6mm supply repurposed for a dishwasher, washing machine and tumble dryer just used 3 single Mk socket they take 2x 6mm don't mess around with additional connectors to drop the cable size
 
Done exactly that before, existing 6mm supply repurposed for a dishwasher, washing machine and tumble dryer just used 3 single Mk socket they take 2x 6mm don't mess around with additional connectors to drop the cable size


2 X 6mm T&E into single sockets? Totally bonkers!!
 
As already said you can get a twin terminal socket for each conductor. If not go for the MK single termination socket. I've got 2 lots of 6mm in before without giving them a hair cut lol. Below is the MK tech spec for a singe termination socket.....


Terminal capacity:
Live, neutral & earth
3 x 2.5mm2
3 x 4mm2
2 x 6mm2 (stranded)
 
2x 6.0mm conductors will go into an MK socket no problem,but as previously stated they need to be cut square and stripped carefully. Insert into terminal as stripped,dont twist the cores up.
Also dont fit the standard lazy a-rse 25mm flush back box,35mm minimum....45 even better.
 
It is difficult to stick 2 6mm2 cables into a socket, however the whole thing is wrong. Assuming the 6mm2 is already in place and therefore the OP intends to use it the best method would be a double socket rather than 2 singles, job done, move on LOL
 
I'd be tempted to put in a sub db so when the client changes their mind about the shed you can add it on easily!
 