Hi,
My electrician removed an old Creda storage heater connected to only 1 off peak supply and installed the SSHE070 but as the power is off peak he cannot set it up.
He connected it up but it has not come on over the off peak period.
Has he missed something?
He asked me to contact Dimplex but no phone number and the online "ticket submission" is no good.
Please can anyone help with this issue I have.
Thanks.
 
Yes your electrician has missed the fact this heater needs a permanent mains supply as well as the off peak supply
The instructions say:
8E8CCD03-8A46-4F8C-A047-5487F516B2B6.png
You need the electrician back to connect it correctly!
 
Hi,
Does it then switch automatically to off peak when the time is right?
Thanks
The on-peak supply probably feeds a timer/control unit and a fan. The off peak supply will power the heating elements, but I suspect the on-peak is needed for the control unit to work, which seems to be borne out by your experience that it doesn't do anything with just the off-peak connected. I'll see what info there is on this.....
 
The on-peak supply probably feeds a timer/control unit and a fan. The off peak supply will power the heating elements, but I suspect the on-peak is needed for the control unit to work, which seems to be borne out by your experience that it doesn't do anything with just the off-peak connected. I'll see what info there is on this.....
Thanks for all your help, I have passed on all to my electrician.
Thanks.
 
Last edited:
You might want to read up on the operation of the controller if you haven't already!

I couldn't immediately see any definitive statement about on-peak power being necessary for it to work, but given the circuit block diagram at the back showing the heating elements apparently controlled through the pcb, I suspect you do need both supplies.
Just been looking around for a customer and I can't find any traditional restricted-supply only NSHs available to buy new, they all seem to need 2 supplies. Makes you wonder why they couldn't have a single unrestricted-supply and some kind of wireless signal when the off peak kicks in.?
 
I have had this recently
You need to have the heater on the 24h supply and then get the switching times for off peak from the supplier- as well as ask them if the switch times stay on GMT or change by an hour in the summer

Good luck getting this from your electricity supplier- I would also ask them to send you it in writing

You then need to enter thesem details in the the relevant setting on the heater and hope it works OK, otherwise the heater will not work / the client gets a massive bill due to incorrect switching times
 
I have had this recently
You need to have the heater on the 24h supply and then get the switching times for off peak from the supplier- as well as ask them if the switch times stay on GMT or change by an hour in the summer

Good luck getting this from your electricity supplier- I would also ask them to send you it in writing

You then need to enter thesem details in the the relevant setting on the heater and hope it works OK, otherwise the heater will not work / the client gets a massive bill due to incorrect switching times
I was thinking you could make something up with a wireless transmitter fired by the off peak supply coming on then a receiver switch on each heater with a contactor or SSR to supply the storage part of the heater, would be clunky though and probably unsightly, unless you figured a way to build the extra components into the heater case somehow...
 
The 24 hour supply doesn't have to be a separate circuit. If there's a socket nearby, it may be possible to spur from it.
All of the the storage heaters I've fitted recently need two supplies due to the need for compliance with the Lot20 directive.
Some can be run on just a 24 hour supply, but as baldy says, it can be tricky to set it up properly.
 
The 24 hour supply doesn't have to be a separate circuit. If there's a socket nearby, it may be possible to spur from it.
All of the the storage heaters I've fitted recently need two supplies due to the need for compliance with the Lot20 directive.
Some can be run on just a 24 hour supply, but as baldy says, it can be tricky to set it up properly.
Thanks for your reply, I will pass on to my electrician.
 

Reply to Connecting a Sunhouse SSHE070 storage heater in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys, Had a call out today about an odd issue with a newish Creda DT storage heater. Basically.. Storage heaters were installed in one flat...
Replies
4
Views
766
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
856
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
420
Hi. I've been asked to install a Dimplex qm150 storage heater for a customer. There is a suitable existing supply for the off peak element...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock