Hello,

Can anyone point me to the specific regulation that using a connector block and electrical tape contravenes?

And what do you use as an alternative?

Thanks a lot!

Lee
 
The situation is that the lights under my kitchen cabinets are twin and earth connected to the flex via a connector block wrapped in electrical tape and shoved up behind the cabinet. I know this isn't adequate but just trying to find which regs it contravenes, and what is the best alternative and why?

Thanks!
 
It needs to be in a suitable fixed enclosure and the flex must be crimped before terminating then it will comply if it isn't accessible for inspection then the whole just and enclosure need to be maintenance free. Alternative methods do exist but as a one off the tackle to do them is expensive so ill omit to bring them up.

There are several regs to cover what i just said so rather than me look em up and list them all just take the advice as good and correct the dodgy workmanship.

As you are a builder what will giving reg no's achieve unless you have a copy yourself and as a good selection of so called sparkies don't have a copy i find it quite surprising you have copy yourself.
 
So terminal blocks in a choc box are acceptable as it gives the connection mechanical strength and protection (526.1), removes mechanical strain on the connections of conductors (526.6), provides protection against relevant external influences (526.7) and means that cores of sheathed cables from which the sheath has been removed ... shall be enclosed (526.8), none of which tape really does. Does that sound right?


I do have a copy of the regs, I'm just trying to learn.
 
So terminal blocks in a choc box are acceptable as it gives the connection mechanical strength and protection (526.1), removes mechanical strain on the connections of conductors (526.6), provides protection against relevant external influences (526.7) and means that cores of sheathed cables from which the sheath has been removed ... shall be enclosed (526.8), none of which tape really does. Does that sound right?


I do have a copy of the regs, I'm just trying to learn.

Close enough ... the flex requires crimping before termination as you have suggested using connectors assuming you meant screw type - and the cable should be suitably retained so any movement or flexing won't apply adverse stress on the termination - either a cable clamp, stuffing gland or in some cases clipping of the cable external to the jointing box.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Durham

Thread Information

Title
Connector block and electrical tape
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
9
Unsolved
--

Advert

Thread statistics

Created
hollerz,
Last reply from
telectrix,
Replies
9
Views
5,073

Advert

Back
Top