Regarding earth leakage tester,
I don't know how to use one , because I don't own one.
Simply because I have never needed one.
Any time I have been called back for a nuisance tripping fault 9 times out of 10 its been :
Dodgy item plugged in like irons , washing machines, extension leads to sheds/garages, any outside socket /light/ pond pump basically anything where moisture is likely.
Fittings being changed for fancy ones or moved for decorating and not done properly, (contemporary metal fittings that don't fit into normal back box depth,which squashes the wires which fall out, screws through wires etc..)
New Lights where there is not enough room to fit loop in/out/sw and again squashed in so they fall out.
If I disconnect circuit on a suspect RCD and the ramp test is less than 15mA I have just changed it.
This was the first time I had something that would have stumped me , as totally random and hardly any load, hence I started looking at buying an earth leakage tester and would have learnt how do use it , just like when I first learnt how to use an MFT,
I would not have give up until I had sussed problem out, and would have come on here to ask advise from people more knowledgeable than me, which is why these forums are so good.
If you think the attitude to admit I don't know something,
Am willing to buy new equipment and try and learn it,
And ask any one with better knowledge to better myself,
"leaves a lot to be desired...."
Well what can I say to that mentality?