totally unacceptable. any appliance > 2.2kW should be on it's own circuit, not the socket circuit. a dedicated 32A circuit wired in 6mm is required.
If it says 7.5kW then it needs to be bigger than 2.5mm cable
It is talking about the total connected load. Can the grill be energised at the same time as the double oven, for example? £100 says it can't be (after all the grill will be housed in one of the ovens).
The load will also cycle a lot as temperature is reached.
So we don't know the real load.
nope. e.g. immersion heater - any appliance.Is it not over 2kw cooking appliance only ?
Hi again, sorry been working away.
had a sparky round while I been away, due to the wooden floor and the in-laws not wanting to take it up, the sparky has said he will put 3 fused Spurs in and spilt the cooker, is this safe ????
Can someone tell me about cooker cables, the in-laws have had a new kitchen fitted, but they have put the cooker on 2.5mm cable, and wired it in to the ring main off a switched fuse ???
the cooker is a range master, for some reason the kitchen fitters took the manual for the cooker ???
but I have download a copy, it states that with both ovens, clock and grill it's 7.5kw (the hob is gas)
the reason I ask is because on Saturday had family party, used the ovens and the fuse blown, not much fun when your half way cooking, I always thought cooker cables are 6mm.
the manual does say 2.5mm to 6mm but to me the lines point to the cores in the cable, if that makes sense
Can't believe we're still on this-
p425 Appendix 15 of BGB, 433.1.103 (iii), cookers, ovens and hobs rated over 2kW must be on their own dedicated radial circuit.
Immersions and space heaters are covered under 433.1.103 (ii)
Read the flipping regs book, reading isn't really that hard, you're doing it now.........
Problem is matey, that Kitchen Fitters don't have copies and think they know best!
Hi again, sorry been working away.
had a sparky round while I been away, due to the wooden floor and the in-laws not wanting to take it up, the sparky has said he will put 3 fused Spurs in and spilt the cooker, is this safe ????