On page 25 does it have the 2.5mm min 6mm max
Discuss Cooker cable in the UK Electrical Forum area at ElectriciansForums.net
totally unacceptable. any appliance > 2.2kW should be on it's own circuit, not the socket circuit. a dedicated 32A circuit wired in 6mm is required.
If it says 7.5kW then it needs to be bigger than 2.5mm cable
It is talking about the total connected load. Can the grill be energised at the same time as the double oven, for example? £100 says it can't be (after all the grill will be housed in one of the ovens).
The load will also cycle a lot as temperature is reached.
So we don't know the real load.
nope. e.g. immersion heater - any appliance.Is it not over 2kw cooking appliance only ?