Discuss Cooker circuit (cable size?) in the UK Electrical Forum area at ElectriciansForums.net
Zdb
Hi guys, I've been given the task of installing a 32A commando socket w/ isolator, which will have a 27A oven plugged into it. It will be on a C32 30mA RCBO. The cable from the oven is 4mm which will have the 32a commando plug fitted to it.
My question is, should I wire the 32A commando socket in 4mm or 6mm? The cable run isn't very long so voltage drop won't be an issue.
Installation method
Length of run
What do your calculations tell you
you using singles? any diversity applicable to the cooker?
then base your calcs on the multicore cable as that will probably have the lowest ccc.
Reply to Cooker circuit (cable size?) in the UK Electrical Forum area at ElectriciansForums.net
The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
Came across a cooker circuit with 10mm and 40A rcbo. Last leg was 6mm. Isolator to outlet. I downgraded to rcbo to 32A to accommodate the 6mm...
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...