i have just bought a range cooker that is dual fuel, its mostly gas but has an electric hob/warmer, in the specs it says the max load is 7.2kw but it has a plug top? i need to put a socket in for it but not sure if i can use the existing wiring and downrate the mcb?

Rob
 
Last edited:
Something does not ring true.
You cannot run 7300 watts on a 13a plug top.
This will need direct connection on a separate circuit.
Normally run in 6mm cable.

are you sure the plug top is not for the spark to light the gas?
 
there is only a plug top, no plate for a fixed connection, the electrical side of it is only ignition and a small hob/plate heater so i would assume it doesnt pull much ampage, just referring to the literature that came with it says max load @ 230v 7.2 kw, which has me a bit confused
 
Is it possible that the user manual covers more than one model of your range and that they do a fully electrical version of it, and you have missed that bit in the instructions lol.
 
No chance! In total 7 kw mate you warmer plate is 13 amp the rest is kw in gas I know I have one
 
agree witrh sedgy. the kWratring for the cooker will include the gas equivalent on kw like they do with your gas bill, convert cu m to kwatts so you can't understand it.
 
if the appliance already comes fitted with a BS plug top from the manufacterer - then the power requirements have already been assessed for you.
 
No insult aimed or intended was just stating a fact
Your plugtop will power your hotplate and warmer that's all
 

Reply to cooker rating in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock