Howdy all,

Went to look at a cooker install today and i though i would run this by you chaps first.

Gas oven with power for clock and ignition, ceramic hob on 32a MCB (no rcd in sight), with a jb on the load side of the switch on a 6mm te. The hob, with fitted flex is connected to this jb.

Also, someone at some point has spurred from this JB with some 2.5 to a single socket which powers the oven.

Personally i cant see anything wrong but im sure one of you will put me straight.

:D

Ta.
 
what's the rating of the hob?
 
I assume the oven that's on this socket wired in 2.5mm with a 32A OCPD has a plug with it's own 1361 in it?
 
I fear many have overlooked your obvious sarcasm.....
 
Last edited by a moderator:
Humor me?
Well the way i read it even with my copious amounts of beer in me on last post (note to self must stop doing posts when ratarsed:eek:) was that the oven was a recent install but maybe Jason can enlighten me on that and a 2.5mm cable had been run off a 6mm jb to a socket, if as i think hes suggesting its a recent edition to the circuit so as to require the need for the rcd to be fitted which he clearly notes it has none, i see no issue with the cable sizing reduction as its protected from overload by any plug top fuse
 
Last edited by a moderator:
but the 2.5 is only protected at the load end by the plug top fuse. it's 32A at the supply end. unfused spur.
 
I would also say it would be a better set-up teletrix that a 6mm cable that is linked to the socket or a spur but a cable can be de-sized if a short piece as long as it is load limited by what it supplies so no risk of overload, the max load would be 13amps if anything else were plugged in to this socket which the cable can handle, this is why you can use 10mm tails to feed a 1way fuse board with say a shower on it thus no need for 25mm tails which wouldnt fit the enclosure, the mcb in this board limits the load so the smaller tails are protected even though they are on the supply side.
 
Last edited by a moderator:
ok so i'm the newbie here but if the spur is not fused untill the plug and it is basically just a 2.5 radial to the socket then you have a 32A mcb protecting that piece of 2.5 twin and earth and no rcd what would happen if there was a fault just below the 32A trip would get a little warm wouldn't it?
Paul
 
When the reasonable argument is made of downstream overload protection,I think it should be judged on whether it formed part of the original design
The socket on 2.5mm spurred off the 6.0mm at the Jb,it could be argued. that as an addition there is no problem
However the cable from the cooker control was for the hob
At a minimum,the socket should have its own supply off the control, and not be tapped into a cable designed for a fixed appliance
 
You raise a good point solo the cable tolorences are well within this limit they are rated to 70 degrees c before any breakdown of insulation and as the 2.5 is rated at approx 24amp going over by several amp wont get it anywhere near but will warm it up, think of this situation elsewhere and you realise its common practice, if you have a ringmain and then spur a socket off it with 2.5mm then effectively you have the same senerio with a front end 32amp overating the cable.The kind of fault that will break the insulation down letting current through just under the mcb rating would be a rare event indeed to the extent that it isnt of concern.
Dont get me wrong i wouldnt personally use this method that jason has come across i would spur with a 6mm to the socket or a fused spur and also give the rcd protection it is required to have.
 
Last edited by a moderator:
When the reasonable argument is made of downstream overload protection,I think it should be judged on whether it formed part of the original design
The socket on 2.5mm spurred off the 6.0mm at the Jb,it could be argued. that as an addition there is no problem
However the cable from the cooker control was for the hob
At a minimum,the socket should have its own supply off the control, and not be tapped into a cable designed for a fixed appliance
I agree its not ideal or maybe not the original design but i recall maybe in one of the onsite guides its a acceptable method to supplying a hob and cooker off one supply as long as the loading is within limits after diversity applied albiet it was shown with a 6mm spur to a socket which is the method i would employ if needed, but if designing and wiring from new then yes seperate supplies to each.
 
The question is could the load be subject to overload.
When we work out current carrying capacities (It) we use either the design current (Ib) or rated current (In). So if the socket is accessible for other uses and not designated, then you would use In as it is subject to overload. However if it can be assured that the load is fixed then we can use Ib or even assume the 1361 In as both are acceptable on 2.5mm
 
Hi chaps,

The oven is all gas, with an electric grill rated at around 2kW, with a digital time clock.

The 32A MCB feeds a 45A DP switch from which a 6mm TE runs to a JB.

From this JB there is the cooker flex connected as well as a 2.5 which feeds a single socket that the gas oven is plugged into.
 