Elmocash

Hi, On a kitchen refit i found the cooker supply wired in aluminium pvc/pvc. I did a temp connection to give the client a working oven for the weekend. The Al cable is solid core of around 4mm, i connected new 6mm T+E in standard strip connectors with brass tunnel and steel screws. Thats a lot of mixed metals, any ideas of a permanent joint of Al/Cu. Cheers, Elmo
 
fit g/box with terminal block(terminals with an internal leaf between core and screw so screw dosn't screw direcly into core)and apply an anti/oxidising paste to each joint.
yours benji
 
Hi, On a kitchen refit i found the cooker supply wired in aluminium pvc/pvc. I did a temp connection to give the client a working oven for the weekend. The Al cable is solid core of around 4mm, i connected new 6mm T+E in standard strip connectors with brass tunnel and steel screws. Thats a lot of mixed metals, any ideas of a permanent joint of Al/Cu. Cheers, Elmo

I would remove it as if you look at the 17th the smallest cable for ally cable is 16mm.
 
Thanks benji , thats the sort of thing i was looking for. There's a lot of stuff from the US about this where it seems ally cable was used more commonly. They use a practice called ' pigtailing' where copper fly wires are attached to the installed aluminium cable at the accessories in a compression sleeve, simillar i should think to the cable joint older spark's have told me about for doing j-boxes on ally cable. The stats for house fires caused by ally cable in the USA seem to have drivern this as a standard fix when ally cable is found on an inspection. I read somewhere ( stats from the US again ) ..your house is 55 times more likely to burn down due to an electrical fault if it is wired in aluminium cable...!, and having seen the photos of roast fittings from the houses that did survive i'm going to rewire the circuit as ian.settle1 has suggested. Thanks to you both.
 

Reply to Copper to aluminium in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Evening all. I've been working on an early 70's house the last 2 days - 1st fix for a lighting alteration, plus minor remedial work on the ring...
Replies
15
Views
3K
I'm doing another EICR, I still don't like doing them, and still seem to attract the weird/unusual/uncommon stuff. This time I'm faced with...
Replies
12
Views
3K
I visited a client about a week ago, an elderly couple complaining that their lounge, hall and landing lights were all flickering simultaneously...
Replies
49
Views
6K
Hi, I build lamps from copper piping and various other bits and bobs (including the occasional trumpet!!). The lamps are made from sections of...
Replies
8
Views
5K
We recently had a thread or two about some cables that were almost certainly tinned copper, but people continued to suspect they were aluminium...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock