blueschill

I have to do an install using trunking which I have nebr used before, I understand there had to be 45% free space inside for heat travel.
so what size trunking do I need to fit two 2.5 t&e cables inside?

As I said I have never used trunking before so it is new to me.
 
OSG page 137

Each 1.5 = 8.0 cable factor
Each 2.5 = 11.9 cable factor
So

So (11.9x4) + (8.0x2) = 63.6 cable factor

Smallest trunking in OSG is 50x38 which has a factor of 767, 45% taken into account.

I'm sure a lot of the guys will say MT2 would be fine.......maybe.

Make sure your playing halo tonight ;)
 
I would also use YT2 for those cables.
Couple of tips for installing trunking. Whether you use sticky back or non sticky, make sure you plug and screw as sticky will eventually peel off. Use proper joint pieces ( tees, flat bends, internal corners etc ) as mitred corners can look afwul on small trunking.
 
~Hey guys thanks for the info I did the job, used mt2 trunking ( also used a chart to get it right Untitled ) with proper joint pieces, and the job looked proper smart and went very well, thanks guys for your help. :)
 
To ask this sort of question you must be a ...........lorry driver or butcher or scaffolder or a dentist or ......... please don't tell me you are an electrician, how can you even think of doing electrical installations for a living when you have to get on "the internet" to ask this GOD HELP US ALL..........
I have to do an install using trunking which I have nebr used before, I understand there had to be 45% free space inside for heat travel.
so what size trunking do I need to fit two 2.5 t&e cables inside?

As I said I have never used trunking before so it is new to me.
 
wahey ! we have a rant lol.
whats your next trick ?

and drop the quals waving tantrum , you'll come off very badly against some regulars on here.
 
Last edited by a moderator:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Correct size trunking for heat dissipation?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
13
Unsolved
--

Advert

Thread statistics

Created
blueschill,
Last reply from
Sintra,
Replies
13
Views
3,187

Advert

Back
Top