Engineer54 - The BEAB standard for manufacturer testing of IT equipment manufactured to BSEN 60950 includes an earth continuity test: "with a current of 10A (BEAB recommend 25A) from an AC source having a no load voltage not exceeding 12V." Although another part refers to 1.5 times current rating of primary fuse. Megger use 9VAC.
So I stand by my comment that a 25A test at <12V SHOULD not damage IT equipment. I have chosen my words carefully and this does not mean WILL not as I do know that when in use and subject to heating cycles, spikes, surges etc on mains and earth, components will weaken over time and may be damaged by such a test. As the impact of damaged IT equipement is high we lessen the risk by testing at a lower current, still using the <12AC source.
If my interpretation of the standards is wrong I please tell me where.
Also as it not always easy to determine if equipment has been manufactured to BSEN 60950 the soft test should not damage any not to this standard.
So I stand by my comment that a 25A test at <12V SHOULD not damage IT equipment. I have chosen my words carefully and this does not mean WILL not as I do know that when in use and subject to heating cycles, spikes, surges etc on mains and earth, components will weaken over time and may be damaged by such a test. As the impact of damaged IT equipement is high we lessen the risk by testing at a lower current, still using the <12AC source.