Paul.M

OK its been a long night shift and I cant be bothered looking in the book, besides I'v never had some one do my homework for before lol.

Here is the set up:- Bar/small nightclub, T+E on tray feeding 8 circuits of rock roses/greggs (6-8 on each circuit). From the rock rose to a pendant lamp holder we have used L+N (no cpc/earth) as the lamp holders are plastic. Some of the 2 core fancy flex are cable tied to the tray. Dose that make it fixed wiring therefore needs an earth/cpc? All are nominal voltage (well 243V) and RCD protected. Dose the full length of the circuit require a cpc when pulled into a rock rose?


As I say, its been a long night and my brain is hurting from the board change lol. I'm off to bed, I'm knackered.
 
I would say no.
The regs require a CPC at all points in a fixed wiring system. Past the plug in rose would not count as fixed wiring IMHO as it is just that, a plug into a socket.
The fitting requires no earthing, so all is good in my eyes.

night night.
 
Glad you said 'No' there Andy, I couldn't make my mind up!
Get out clause, Paul, think of it as 'Secured Wiring' rather than 'Fixed'. :-)
 
Lol only my opinion to the best of my knowledge of the regs, without actually opening the damn thing and looking. Let's just say I'm right until someone trumps me with a reg.
 
Andy and Archy, we are singing from the same page, not hard wired so BS7671 not applicable. This got me scratching my head at 4am lol. Still does not feel right, some of the runs are up to 9m away from the rose and no cpc? Just did not seem right and I would have liked to install 3 core but the bar sourced this fancy flex and just got 2 core.

Main contractor called his scam helpline and they scratched their head on this matter so its not just me lol. Came up with the same conclusion but it got them thinking.

Thanks gents.
 
i agree with above, but it's bad design to have the fittings so far from the roses.
 
You do not have a CPC from class 2 transformers to the light fittings they supply, so from the ceiling rose to the class 2 light as it is a final connection I see no need to worry about a CPC. However I hope you sampled the local brew before you left site lol
 
i agree with above, but it's bad design to have the fittings so far from the roses.

Yep agree... I wonder if they used LSF T&E in this nightclub?? Pretty sure that's a requirement now for confined public places such as Disco's, Nightclubs and the like.
 
However I hope you sampled the local brew before you left site lol

I popped in on Saturday on my birthday toby around town and they supplied us with quite a few free drinks. Had a free pint last night at another pub with Phil. Mad rush to get a pub open for today and lighting faults all over the place. When we finished at 2 am the landlord pulled us a pint, sat down and we all had a pint and a CIG in the pub!!! Wow, remember when adults could do such things in an adult environment?
 
Yep agree... I wonder if they used LSF T&E in this nightclub?? Pretty sure that's a requirement now for confined public places such as Disco's, Nightclubs and the like.

Its the only LSF in the place lol, everything else is pvc. We also noticed the feed to the fire alarm was in pvc so changed it to FP200 like it should have been in the first place.
 
and another thing as well when using seperate CPCs...:

if the G/Y is unprotected (sheathed) or does not form part of a cable (flex)...then its a min of 4mm CSA...
 
As long as the lamp holder as no exposed conductive part then Paul you can evoke regulation 411.3.1.1 Merry Christmas mate
 