Hi guys this is my first post so bear with me, but what are your thoughts on cross bonding in bathrooms? Do you still need it if the installation is rcd protected with adequate main equip potential bonding is present?
 
not if disconnection times are within limits.
 
As long as all extraneous conductive parts are effectively connected to the MET then no need for supp. equipotential bonding.
 