bjl

-
Reaction score
0
im changing over the old danfoss 103 mechanical timer over to the danfoss FP75 programmer. It is a combi boiler so hot water side wont be used just wanted to check on wiring. The connections are

103 timer common terminal 3 linked to live
'on' terminal 1

FP75 programmer CH on terminal 4
CH off terminal 2

just to check where does cable on timer 103 terminal 1 'on' marked go on the programmer ?? CH on or off??
 
This programmer may not be suitable, as it has no dry relay contacts. The fp75 has only switch live outputs for CH and HW
 
Connect it to terminal 4 CH on

Good tip on damaging his boiler......A combi requires dry contacts as already stated. Lee sparks has posted 2 diagrams, one for volt free timer (which is required) and one for the Danfross fp75 which has switch live. (which will not work)
 
Good tip on damaging his boiler......A combi requires dry contacts as already stated. Lee sparks has posted 2 diagrams, one for volt free timer (which is required) and one for the Danfross fp75 which has switch live. (which will not work)

But the OP states that the live is linked to the common of the volt free switch on the existing programmer
 
Good tip on damaging his boiler......A combi requires dry contacts as already stated. Lee sparks has posted 2 diagrams, one for volt free timer (which is required) and one for the Danfross fp75 which has switch live. (which will not work)
I don't know what you mean by "dry contacts" if you mean volt free then the OP already said that live was linked to common on the 103 which means the boiler is mains switched.
So not likely to damage the boiler at all!
 
I don`t know any combi which works on switch live, all I seen are volt free switching to timer then stat.
The op states this is a timer he has not what was fitted, so link was on backplate
 
Last edited:

Reply to Danfoss 103 mechanical timer to FP75 programmer in the Central Heating Systems area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock