im changing over the old danfoss 103 mechanical timer over to the danfoss FP75 programmer. It is a combi boiler so hot water side wont be used just wanted to check on wiring. The connections are
103 timer common terminal 3 linked to live
'on' terminal 1
FP75 programmer CH on terminal 4
CH off terminal 2
just to check where does cable on timer 103 terminal 1 'on' marked go on the programmer ?? CH on or off??
This programmer may not be suitable, as it has no dry relay contacts. The fp75 has only switch live outputs for CH and HW
Connect it to terminal 4 CH on
Good tip on damaging his boiler......A combi requires dry contacts as already stated. Lee sparks has posted 2 diagrams, one for volt free timer (which is required) and one for the Danfross fp75 which has switch live. (which will not work)
But the OP states that the live is linked to the common of the volt free switch on the existing programmer
I don't know what you mean by "dry contacts" if you mean volt free then the OP already said that live was linked to common on the 103 which means the boiler is mains switched.
So not likely to damage the boiler at all!
I don`t know any combi which works on switch live, all I seen are volt free switching to timer then stat.
The op states this is a timer he has not what was fitted, so link was on backplate
Reply to Danfoss 103 mechanical timer to FP75 programmer in the Central Heating Systems area at ElectriciansForums.net
Hi Guys Changing my heating/water programmer and im stuck on the wiring ive gone from a danfoss to a Drayton and the wiring description is...
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Hi. We are looking at installing a Wiser smart heating system inc. trvs We are currently electric only, with normal rads and a Heatrae sadia...
A question if I may before I dive in. I have an old gravity fed CH system which thanks to members here in the past - works very well. It has a...
Hello there, I’m in the process of mapping out a relatively standard S-plan system for my parents central heating and hot water system. Not sure...