This came with the rcb’os,providing a upfront Rcd is used,it’s ok-ish,I realise discriminating may not be ideal,but what else can you do,on a TT system.

yea,your talking about the N/E faults that may happen,discrimination will occur when there’s a L/E fault.
Who on earth uses double pole rcbo’s,.

Not double pole but switched neutral. These would of done the job.
Wylex NHXS1B32 32 Amp 30ma Type B 1 Module RCBO - Edwardes - https://www.edwardes.co.uk/en/products/wylex-nhxs1b32-32-amp-30ma-type-b-single-pole-1-module-rcbo-?utm_medium=google_shopping&utm_source=google&utm_campaign=google_shopping&gclid=EAIaIQobChMIxemvxrWc2wIVypPtCh23egO4EAQYASABEgLWBfD_BwE
 
This came with the rcb’os,providing a upfront Rcd is used,it’s ok-ish,I realise discriminating may not be ideal,but what else can you do,on a TT system.

yea,your talking about the N/E faults that may happen,discrimination will occur when there’s a L/E fault.
Who on earth uses double pole rcbo’s,.

I do, TT quite common around here so I use an SBS board.
 
Ok,if the fault happens on the 30ma protected circuits,theses would trip before the time delay Rcd.
That’s why the time delay Rcd is installed.
It’s no-different set up than the above literature supplied by the manufacturers.
I can see your points about the N/E scenario,thinking that would be the worst case.
When this set up was introduced years ago,it worked well,preventing complete disconnection, of power.
 
Ok,if the fault happens on the 30ma protected circuits,theses would trip before the time delay Rcd.
That’s why the time delay Rcd is installed.
It’s no-different set up than the above literature supplied by the manufacturers.
I can see your points about the N/E scenario,thinking that would be the worst case.
When this set up was introduced years ago,it worked well,preventing complete disconnection, of power.
You are literally talking milli seconds before the upfront RCD trips aswell as the RCBO. what's the installation method of the distribution circuit feeding the loxone?
 
Ok,if the fault happens on the 30ma protected circuits,theses would trip before the time delay Rcd.
That’s why the time delay Rcd is installed.
It’s no-different set up than the above literature supplied by the manufacturers.
I can see your points about the N/E scenario,thinking that would be the worst case.
When this set up was introduced years ago,it worked well,preventing complete disconnection, of power.
Yeah but even when the downstream RCBO trips the N-E fault will still remain and therefore will trip the main RCD after the time delay because the RCBO will only disconnect the line of the CCT the neutral and earth are still in the bars and the fault will be seen by the RCD main switch. IMHO the best way to sort it and achieve discrimination is to change the MCB to an RCBO and have an upfront isolator rather than a main switch.
 
Yeah but even when the downstream RCBO trips the N-E fault will still remain and therefore will trip the main RCD after the time delay because the RCBO will only disconnect the line of the CCT the neutral and earth are still in the bars and the fault will be seen by the RCD main switch. IMHO the best way to sort it and achieve discrimination is to change the MCB to an RCBO and have an upfront isolator rather than a main switch.
Yea I can see where everyone is coming from,we are talking about a n/e fault here,I know it’s on aTT system,but realistically
These faults may be happening all the time,on most earthing systems,with negligible currents flowing.
N/e faults have always been a pain,& so be it if all power is disconnected,also if the rcbo disconnects that circuit surely that prevents any fault being on that circuit ie:N/E.,no current will flow to Earth ,arguing the fact the rcbo will trip on a N/E fault.
This is getting mighty confusing.
 
Ok,if the fault happens on the 30ma protected circuits,theses would trip before the time delay Rcd.
That’s why the time delay Rcd is installed.
It’s no-different set up than the above literature supplied by the manufacturers.
I can see your points about the N/E scenario,thinking that would be the worst case.
When this set up was introduced years ago,it worked well,preventing complete disconnection, of power.
Yeah but even when the downstream RCBO trips the N-E fault will still remain and therefore will trip the main RCD after the time delay because the RCBO will only disconnect the line of the CCT the neutral and earth are still in the bars and the fault will be seen by the RCD main switch. IMHO the best way to sort it and achieve discrimination is to change the MCB to an RCBO and have an upfront isolator rather than a main switch.
Yea I can see where everyone is coming from,we are talking about a n/e fault here,I know it’s on aTT system,but realistically
These faults may be happening all the time,on most earthing systems,with negligible currents flowing.
N/e faults have always been a pain,& so be it if all power is disconnected,also if the rcbo disconnects that circuit surely that prevents any fault being on that circuit ie:N/E.,no current will flow to Earth ,arguing the fact the rcbo will trip on a N/E fault.
This is getting mighty confusing.
even with no current flowing the act of joining the N and earth will trip the rcd try it on a dual rcd board switch off the mcb for say a socket circuit and short N-E the RCD will trip so it makes no difference if the RCBO trips in that board it will still trip the upfront RCD it isn’t compliant with BS7671 if you haven’t achieved discrimination in all fault conditions of final circuits and should be noted as a departure on the EIC along with an attached risk Assessment
 
That applies to all time delay DB’s.If the mcb is changed to a rcbo,then a main switch installed,IMO,that’s makes it worse,N/E remains.
 
That applies to all time delay DB’s.If the mcb is changed to a rcbo,then a main switch installed,IMO,that’s makes it worse,N/E remains.
But it will still only trip the affected CCT the fault will remain until rectified but the the circuit will not be able to be energised which should mean that no dangerous current should flow from nuetral to earth
 
Ideally, you should swap the RCBOs in the Lighting panel for MCBs, swap the 63A MCB for an RCBO and swap the upfront RCD for a main switch.
Then again, is it really worth it?
 
My issue with the Lewden boards is the advised torque settings, I have two torque drivers and with either if I torque them to manufacturers settings it has a tendency to damage the rcbo screws.
Never had a torque driver...and never had a problem.
We should go back to double screwed terminals.....it'd give everybody two chances of getting at least one right. Like these, maybe. :cool:
IMG_1434.JPG
 

Reply to DB installed connected & tested in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I've installed a Lorex doorbell recently, but it is not turning on. I did some tests using a multimeter and this is what I found...
Replies
5
Views
1K
Hi, I have a dual RCD board made by Hager installed a couple of months ago. It is high integrity, which I understand to mean RCBO’s can be...
Replies
17
Views
3K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K
I’m a trainee electrician and would really appreciate the benefit of someone’s skill and experience on the following: Our house is a TN-C-S (100A...
Replies
70
Views
6K
Hi all, So I’ve been having a strange fault in my house which has just appeared over the past few days. About a month ago I moved my pc set up...
Replies
136
Views
14K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock