This came with the rcb’os,providing a upfront Rcd is used,it’s ok-ish,I realise discriminating may not be ideal,but what else can you do,on a TT system.

491382E2-7CEE-4D2D-B27D-441EBF1028E6.jpeg
 
This came with the rcb’os,providing a upfront Rcd is used,it’s ok-ish,I realise discriminating may not be ideal,but what else can you do,on a TT system.
Trouble is unless they are double pole rcbos then you have provided no discrimination.....
yea,your talking about the N/E faults that may happen,discrimination will occur when there’s a L/E fault.
Who on earth uses double pole rcbo’s,.
 
But N/E faults are mighty common? Meaning that one ANYWHERE on that install will cause the upfront to trip loosing the entire installation.

imo that doesnt comply with the regs so either DP rcbos or an alternative design should have been considered.

Also imo on TT with a full rcbo board the 100ma S is not required upfront so youd actually be better off swapping that mcb for an rcbo and the upfronter to a main switch...
 
Last edited by a moderator:
Ok,but then neutral to earth faults will not be disconnected at all,they will remain,unless DP rcbo’s are used.
The reasoning for the time delay is,discrimination for the lighting panel,which have its own rcbo’s.
 
A neutral fault on that circuit,will trip the individual rcbo’s on the lighting panel,before tripping the time delay Rcd.
yes but as Suffolk spark has said it will still trip the upfront RCD so there is no discrimination in the event of a neutral earth fault.

Neutral-earth fault=loosing every circuit.
 
This came with the rcb’os,providing a upfront Rcd is used,it’s ok-ish,I realise discriminating may not be ideal,but what else can you do,on a TT system.

yea,your talking about the N/E faults that may happen,discrimination will occur when there’s a L/E fault.
Who on earth uses double pole rcbo’s,.

Not double pole but switched neutral. These would of done the job.
Wylex NHXS1B32 32 Amp 30ma Type B 1 Module RCBO - Edwardes - https://www.edwardes.co.uk/en/products/wylex-nhxs1b32-32-amp-30ma-type-b-single-pole-1-module-rcbo-?utm_medium=google_shopping&utm_source=google&utm_campaign=google_shopping&gclid=EAIaIQobChMIxemvxrWc2wIVypPtCh23egO4EAQYASABEgLWBfD_BwE
 
This came with the rcb’os,providing a upfront Rcd is used,it’s ok-ish,I realise discriminating may not be ideal,but what else can you do,on a TT system.

yea,your talking about the N/E faults that may happen,discrimination will occur when there’s a L/E fault.
Who on earth uses double pole rcbo’s,.

I do, TT quite common around here so I use an SBS board.
 
Ok,if the fault happens on the 30ma protected circuits,theses would trip before the time delay Rcd.
That’s why the time delay Rcd is installed.
It’s no-different set up than the above literature supplied by the manufacturers.
I can see your points about the N/E scenario,thinking that would be the worst case.
When this set up was introduced years ago,it worked well,preventing complete disconnection, of power.
 