Hello everyone,
I saw in the hospital every circuit has 2 separate cpc, same size, sometimes different. I'm wondering. How we can do the dead test in this case? R1+R2 whith 2 cpc combine, but IR test 2 cpc separate? what result will be sign in test sheets?What in case if there are 2 different sizes of cpc on the one circuit?
Thank you for your opinions.
 
The IR test would be with all CPCs connected to the MET.

The other tests I don't know for sure, but I would guess a separate R1+R2 test for both CPCs, and record the highest result and smallest conductor.
 