but you will find lots of peeps with forthright views who will defend them vigorously.
Cheers
Yea, I guess that's the point of the forum eh?
but you will find lots of peeps with forthright views who will defend them vigorously.
Cheers
Hi, should have explained, I have a rig I made up I use sometimes, its basically an rcd adaptor that I wire into and plug into a socket, when I did this it tripped
Ok, so apart from the disagreements on what's right and wrong and what certificates are needed, which has definitely been dealt with, I think everyone has missed an important point,
firstly, you've done IR tests and you know that whatever is wrong with the circuit, the readings calculate out to an acceptable value, so end of you should be happy to connect this to an Rcd. but you are relying on a home brewed tester to test whether its safe to connect to Rcd, I would look here for your answer. Your calibrated tester is telling you everything you need to know