HappyHippyDad

-
Esteemed
Arms
Supporter
I will/may be burying 16mm SWA in concrete to route it to an outbuilding (for the kiln I have just been chatting about!). This will be getting driven over by cars. Is there an ideal depth for this? Also, does the SWA require any further form of protection?
 
i'd put it in rigid ducting 12" deep with sand, then the ducting takes the weight of the traffic and you have the option of rewiring should it ever become necessary.
Pretty deep then! A lot of concrete for me to drill out. Makes sense though.
 
suppose you could go shallower. not likely to be dug up. the concrete will only be a few inches anyway, then hardcore or just plain earth.
 
Maybe you could use a mole under the existing concrete if you can dig a pilot trench at either side.
The thought of that scares me silly! ?

In fact, I'm thinking of passing the job purely based on the trench. There looks to be pipework all over the place, some of which may be under the trench. It would only be perhaps 120mm wide and perhaps 3m long but the thought of hitting a pipe does worry me.

Also, how to cover the trench whilst the concrete is setting to allow traffic to pass over?

Perhaps a builder would do this sort of thing and I could contract it out?

It's a bit outside my role. I'm used to changing consumer units and wiring up conservatories!
 
I would agree with all of the above get a contractor in to do the groundwork and definitely put a duct in if only for future adaption.
Or get a mole service to do the hole, at least the above should have all the necessary insurance for that type of work! Plus if they hit something it's their problem!
Sy
 
Pretty deep then! A lot of concrete for me to drill out. Makes sense though.
12 inches isn't very deep.... if the cable is running under a road in the same direction as traffic we usually go around a meter deep in duct to reduce 'cable creep' caused by cars and lorries especially. If the cable is running across the path of the traffic then creepage won't be an issue so we'd usually go around 600mm deep (2ft). If it's a private driveway then 600mm regardless of direction would usually be good.

Also we wouldn't use concrete for fill, if the substrate is sandy and prone to water errosion we might mix a small ratio of cement in with the fill (maybe a 10 or 12 to 1 ratio of fill to cement) to give it some extra stability against future water errosion. As per UNG don't forget the yellow and red hazard tape above the cable.

If the distance is only 3 meters and the ground is free from rocks and boulders we regularly mole it ourselves by digging a hole or more like a pit either side of the road and using a rigid 25mm hose with decent water pressure inside a 40mm HDPE duct and basically work the hose and the duct backwards and forwards through the sand/soil until it finds its way through. This method has saved us a lot of money in the past, so much so that we bought a cheap petrol driven water pump and a 1 kilolitre water tank specially for this purpose, but it's far from guaranteed though. I'd guess we've had about a 75% sucess rate and there's been several occasions where it's not worked and we ended up getting a proper moling company in so make sure you cover that eventuality when you quote.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
-
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Depth to bury armoured cable in concrete with vehicles passing over?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
11
Unsolved
--

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
Marvo,
Replies
11
Views
9,693

Advert

Back
Top