Discuss Difference in amperage though household meter question in the UK Electrical Forum area at ElectriciansForums.net
Hi,
I have just joined as I have a non urgent but nagging question...hope you guys can give me peace of mind!
Thank in advance.
I have just checked the amperage coming in on the meter tails prior to the meter (Between the main fuse and the old style dial meter) this is 0.85 amps. However the measured amperage in the tails between the meter and the consumer unit (actually between the meter and an old 50mA RCD that then goes onto the consumer unit) this is 0.97 amps. Why the discrepancy?
Any thoughts/revelation or 'that should be bleeding obvious mate' answers?
Hi,
Thank in advance.
What sort of test equipment was used to check the current
Assuming you are using a clip on ammeter, these are not all that accurate. Depending where the conductor is in the jaws can affect the reading.
In theory the current going into the meter should be slightly higher than that coming out as it will include the current for the voltage coil. The voltage coil is connected before the current coil so you don't pay for the current it uses. The current for the voltage coil will be very inductive so that may also affect the reading.
I noticed once on a job that even though the tails out of the meter to the CU were disconnected, the meter was still spinning. I only noticed it because i heard it spinning :oops:
Hi, thank you for your response.
Your right, I am using a clip on meter, but I have checked multiple times and I get the same readings every time, so its very repeatable. I would have expected the supply side to show the higher reading as you say the meter must use a fraction of power. I was just surprised to see the higher current on the 'wrong' side and its quite a large percentage higher.
Serves me right for messing around in the house with meters when I should be gardening :)
I suspect that the missing 0.12 amps is going down the Earth bonding conductor. This is very common in PME areas. Measure that. Also check the Neutral-Earth voltage (ideally it should be zero - but I bet it is not). It does not sound like a worrisome problem.
I once found over 300 amps returning down the Earth route (in a commercial premises - and only 20 amps down the Neutral main feed conductor). That was worrisome! Turned out to be due to a corroded u/g main untility feed XLPE cable.
I will check the N-E voltage later and let you know...thanks again.
If it's a TT system then the current returning via earth should be almost zero as there should be no connection between earth and the live conductors (other than filtering caps etc that can cause a small leakage.)
You are correct if there are no wiring problems. For filter caps (etc) it should be a max of less than 1 mA/device (cookers and IT equipment can be a few mA). So nowhere near the 120 mA apparently missing.
However, even a TT supply Neutral is connected to Earth at the distribution transformer. If there is a short or low resistance connection between the house Neutral and the local ground Earth, then stray current can flow (immersion heaters are prone to cause this type of N-E fault). If his clamp-meter readings are correct, then I would take a bet that the "lost" current was probably going via the Earth connection. Should be easy enough to determine using a suitably sensitive and accurate clamp meter.
Another thought is... 'an old 50mA RCD'?? Is that what the protective device is? Or is it an old 50 volt voltage-tripping ELCB that sits between the Earth spike and the CU Earth busbar? That would explain why the '50 mA RCD' is not tripping. That was what used to be fitted in ages past. I have seen plenty in old houses in rural locations.
Another concerning thought - Earth is to an old lead water pipe - only house on the Estate like that now... are you sure - do all the other houses have proper Earth Rods or were they upgraded to supplied PME Earths by the network company sometime in the past? Your water pipe should be formally tested.
Although 120 mA is not a large stray current, it does represent about 30 watts of power - so the cause really should be tracked down and remedial action taken.
So, sorry, it sounds as if you should get a full EICR test carried out.
I think there's some crossed wires, would be helpful for the OP to clarify. He does not seem to be talking about earth leakage at all, but about the supply current. I.e. he has switched off (nearly) all of his appliances and the supply current from the service cable is 0.85A, as measured by putting the clamp meter around either the line or neutral meter tail alone (not both) on the supply side of the meter.
But the current between the meter load side and upfront RCD is 0.97A, measured likewise. So his query is not about earth leakage but the difference in the line conductor current upstream and downstream of the meter, and far from going missing, it appears that more current is coming out of the meter into the RCD than it is drawing from the service head. If I am understanding this question correctly, it cannot relate to earth leakage because the meter cannot create any, not being earthed.
There is a possible explanation. The small load measured is likely a few timeswitches, PIRs etc that are still on when all normal appliances are turned off. These often have capacitive power supply droppers, which have a strong leading power factor. There is also usually some capacitive leakage current from suppressors in other 'live-but-off' appliances and the wiring itself. The clamp ammeter is correctly measuring the total of these at 0.97A. The kWh meter is also drawing current through the supply side tails for its voltage coil, but as R-fur points out, this is inductive with a strongly lagging power factor, so this current is more than 90 degrees out of phase with the house load. Hence, the input current to the meter is lower because it is compensating for the leading power factor of the house load.
If rather than current, the OP measured the power before and after the meter, he would likely find that although the current before is lower, the real power is higher, due to the dissipation in the voltage coil. In any case, measuring the currents without also comparing the phase, when the power factors are extreme, can give odd-looking results.
Also as mentioned above, there is a risk of measurement error with a clamp at low currents, including from stray fields from the magnetic circuit of the kWh meter. A significant part of the difference in readings could be due to measurement error.
Thanks, Lucien. A thoughtful and interesting contribution.
I strongly agree that local magnetic fields (espercially from the meter if an old rotating disc type) would be likely to affect the clamp-meter reading - though the OP says he has measured multiple times and the values are very consistent. It does depend on the quality and sensitivity of clamp meter and the harmonic content of the current waveform.
I do not understand how the PF can affect a clamp-meter current reading. The clamp meter is just measuring the magnetic field from the current flow. It is not calculating power. So it does not matter what the phase relationship of the current waveform to the voltage waveform is. A really bad PF can lead to higher harmonic content and therefore erroneous readings (especially on cheap clamp meters).
An investigation by a competent and knowledgeable qualified electrician is really needed if the OP wants to resolve this. Especially as his main Earth is an old lead water pipe and most other houses nearby have utility supplied main Earth connections.
Are the cables being measured a similar distance apart ,any curves nearby --
(forming a partial turn rather than a long straight run) ... Expecting something like this as a source of error .
Neutral - earth pd ,with house in OFF condition
may have some clues !
I'm not saying power factor is affecting the readings, rather that it is responsible for the apparent anomaly that the input current to the meter is lower than the output current. My theory is that each reading is correct in itself, and the input current is indeed lower, but since the voltage coil magnetising current is heavily lagging, if the house 'standby' current is leading then subtracting the meter output current from the meter input current can yield a negative result even while both the house and the meter coil apparent power is positive. If the OP replies and confirms that we've understood correctly, I'll draw a phasor diagram.
Ah, I now follow. IF (quite a big if in my opinion) the inductance of the meter coil is enough to improve a bad capacitive PF and move it closer to unity, then the current on the supply side will be lower for the same total power. Yes, that is true. It would be very interesting to measure and calculate the PF in both places.
I may have a play with an old meter and some low current capacitive loads over the w/e.
Hi,
Its a TT system but it does not have a dedicated earth rod. Its earthed via the old copper going into lead mains water pipe. I am the only person on my estate still on lead and I have it all to myself and I have a long drive so there is plenty underground.
I don't think you should be using the water supply pipe as your earth electrode. 542.2.6
Reply to Difference in amperage though household meter question in the UK Electrical Forum area at ElectriciansForums.net
Hello everyone In September 2023 I rented a beautiful 3 bedroom apartment, with all electric supply, no gas powered appliances. I noted down the...
Hi looking for a bit of advice about an issue I have with some work arranged by a social landlord. The landlord had to fit a new consumer unit but...
4K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
4K
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...