If testing a property which has a ring with 2.5mm/1mm t&e (old cable) and 2.5mm single core cables in conduit (addition), how would you record this on the EICR? As for the 1mm earth on the ring circuit, would this be a code 3?
I would record the smallest conductor size in each case.
Why does the size of the cpc warrant a code ?
Record the worst case part of it, and possibly add a note to explain
If it's is not big enough then it warrants a code, but if it is big enough then it does not. You need to apply the adiabatic equation to establish whether it is big enough or not.
I don't think you could justify a C3 regardless, it will either be big enough or it won't so it's either fine or a C2
Table 2D picture
On an older 2.5/1mm CPC RFC whether it's acceptable or not will depend entirely on the Zs measurement, it would take a pretty big circuit to get a reading that would be too high and hence not ensure disconnection in the required time under earth fault conditions. [And with the requirement for 30ma RCD protection for nearly everything under the sun now it's all a bit academic really - if there is one in place for the relevant circuit]
I know Dave, but that's why we have rings.
It's how we can protect 2.5 with a 32 amp mcb. because it is in effect 2 x 2.5 so 5mm.
If that was the case then we could use a cable with 16A ccc for the ring couldn't we? (32/2=16) but instead the minimum ccc of a cable in a ring is 2/3 the rating of the OCPD.
Still less though Dave. We are guded in the regs re ring circuits conductor size.
I'm just trying to help the op to understand how it is that you can have smaller conductor size than would normally be called for.
The normal reasoning for ring cable CCC doesn't apply here though. The continuous load on any leg of a ring is usually less than the OCPD rating because the individual loads are distributed along its length, and in any case can't all be at a single point. However the adiabatic criterion is used to check whether the cable will be raised to a damaging temperature while the OCPD clears a fault, and a fault does occur at a single point. If that is near the end, then most of the fault current will flow through one leg and the 1mm² will have to deal with the B32 by itself (which it will if the disconnection is rapid). In fact with rough figures for K²S² and I²t it might be in under all magnetic trip conditions if Zs is...
E2A I would record all sizes of CPC present, otherwise figures might look wrong when read away from site and compared to one stated size of CPC.
But he's not questioning ring final circuits. He's questioning the use of the old 2.5/1.0 twin/earth instead of the modern 2.5/1.5 twin/earth