Ok to confuse things more the Ze test is 0.11 ohms - it is not TT.
That earth you can see is 100% definitely the gas pipe bond.
That earth you can see is 100% definitely the gas pipe bond.
Put it all back together, clean your finger print and any DNA from the area, claim you had amnesia if anyone says anything, you shouldn't be frolicking about inside the head it's not yours to play with.Hello all,
I've recently put a new circuit in a house and when filling out my EIC, I needed to access the service head (attached).
I'm relatively new to this and I'm struggling here.
In order to access ANY part of this, you have to pull the main fuse and I had to cut a few metal tallys off. As you can see on the left is where the main fuse sits, to the right there is a cover for the MET and underneath is a cover for the incoming cables. The black box between the meter and thefuse housing is not removable - I can't see where the main earth is. The earth cable you can see is bonding from the gas pipe.
Also, immediately I thought it was a TNS system but it gets quite strange. The what looks like SWA is not SWA, it looks and feels like copper!! IT DEFINITELY isn't steel. Additionally, I can't find a neutral anywhere, I can't see if it is in with the red incoming wire but I'd be pretty surprised if it was.
Could the copper SWA (I know) actually be the PME neutral and we are actually looking at a TNCS system here?
Either way, I have never seen anything like this cable before.
Thanks in advance, I genuinely don't know if I'm just being stupid or inexperienced here but I'm kinda stuck with a way ahead.
View attachment 35655
View attachment 35656
View attachment 35657
Ok to confuse things more the Ze test is 0.11 ohms - it is not TT.
That earth you can see is 100% definitely the gas pipe bond.
Don't think that's the gas bond Westy thats the main earth to the CU and OP for info that cable is a concentric cableAre you sure that is the gas bond, what Ze have you got.
Put it all back together, clean your finger print and any DNA from the area, claim you had amnesia if anyone says anything, you shouldn't be frolicking about inside the head it's not yours to play with.
Ok to confuse things more the Ze test is If that is a Gas bond, how did you measure Ze without verifying the earthing conductor 0.11 ohms - it is not TT.
That earth you can see is 100% definitely the gas pipe bond.
Think that's the main earth to the cu, any bonding conductors will/should be on the earth bar in the cu imoIf that is a Gas bond, how did you measure Ze without verifying the earthing conductor
Was that 'gas' bond been disconnected when you did your Ze test?
OP, as already advised by members, think you just need to go back to basics, and verify earthing conductor and main bonding conductors, just in case you've made a mistake. We are all human.
I understand that I may have been hasty to take apart the service head but I have a job to do and I don't want to be wasting time. I'm not going to lose any sleep about cutting some tallies off. I'll phone up the suppliers, If they're going to get upset about it then I'll take it up with them.
Now to sound like a complete -------: while I'm new to the domestic game (and service heads!), I am an electrical engineer trained to degree level through an apprenticeship with 15 years experience in industrial electrics.
Think that's the main earth to the cu, any bonding conductors will/should be on the earth bar in the cu imo

Yep, I'm going to start again, this is turning into a mess.
Thanks for all the advice everyone.
Then you should already be aware of concentric cable, test methods for establishing earthing arrangements, investigation methods for establishing methods of earthing, and remedial action to be carried out to rectify earthing problems.
I'm not belittling your qualification or experience, but degree or no degree, there still exists the probability of not having sufficient training for the task you are doing.
If it really is only connected to the gas then installer has got their wires crossedDon't think that's the gas bond Westy thats the main earth to the CU and OP for info that cable is a concentric cable