davesparks
16mm earth on any installation where the tails are up to 35mm so being either 4 or 6mm is way undersized
Nonsense, where did you get that from? The size required is calculated using the adiabatic equation and subject to a minimum of 4mm if I remember correctly.
16mm would be the size you install if you choose to select the conductor size rather than calculate, but you cannot use this method to assess an existing installation as undersized.